I have a 4 ton blower on my carrier furnace...I'm getting ready to put a Central ac ( goodman ) in. My question is do i use a 3.5 ton coil or a 4 ton coil. Will I see any significant difference between the coils?

brianbrb
01-28-2006, 07:20 AM
you need to have a load calc done to determine your cooling size, just because you have a four ton blower doesn't mean you need four tons of cooling,put a call in to a contractor so it is done right

beenthere
01-28-2006, 07:53 AM
Your contractor will know what coil to match up to what ever size OD unit. After he knows what size A/C your house needs.

hvac hero
01-28-2006, 09:02 AM
A lot of times we oversize the indoor coil by a half ton. If putting in a 3 1/2 ton condenser, then we install a 4 ton coil. Some manufacturers like Rheem dont even sell a 3 1/2 ton coil. You have the option of changing out the metering device i guess to a little smaller one. But I doubt you'd ever know the difference.

air2spare
01-28-2006, 09:16 AM
that a Goodman 3 1/2 ton condenser even puts out 36K of BTUs. Do a load calc then an ARI match your equipment to the load.

hvac hero
01-28-2006, 12:01 PM
Originally posted by air2spare
that a Goodman 3 1/2 ton condenser even puts out 36K of BTUs. Do a load calc then an ARI match your equipment to the load.

LOL @ that

blkwolfpac
01-28-2006, 04:02 PM
thanks for the info