View Full Version : Fan Delay for AC - Issues with new board/thermostat



sparkhvac
10-01-2011, 09:45 AM
ISSUE: Thermostat seems to be sending fan and cool on AC request and is overiding the furnace board settings of cool delay.

EQUIP: Furnace board - Honeywell ST9120B,U; Thermostat - Honeywell RTH8500

ASK: Can I configure this to have the board control the fan and not the thermostat without removing the G wire.

DETAILS:
I recently had my furnace board replaced and have an issue with the COOL ON DELAY. Before this new board there was a 30 second delay. The new board supports this and I have set the DIP settings to 30 seconds, however the fan now comes on instantly when it calls for cool.

If I remove the G wire the process works fine (so it appears that the thermostat is sending for the fan on AC). I am not sure why this worked on the old board, but I don't want to leave the G off as I like to run the fan all the time.

Thanks!

timebuilder
10-01-2011, 09:47 AM
Have your AC contractor configure your thermostat to have the system controlled as you would like.

Mr Bill
10-01-2011, 10:35 AM
I don't want to leave the G off as I like to run the fan all the time.

Thanks!

Why is the delay important if you run the fan all the time? also running your fan all the time in a humid climate is terrible for latent control.