What factors affect moisture (sweating) inside the flue of an 80% furnace installed in a basement?
.

RIGUY
09-29-2011, 09:47 PM
below 130degree flue gasses that wont happen at 80% tho check the flue gas

wogpa67
09-29-2011, 11:02 PM
short run times = the answer

DirkRoper
09-30-2011, 08:32 AM
Not enough heat. Did you downsize the furnace? I've seen moisture run down the flue and fry a circuit board.

smooth_operator
09-30-2011, 01:20 PM
Flue gas temp, flue type, flue size, draft.

Kenoo8
09-30-2011, 02:19 PM
Are you running the flue into a chimney or other concrete or brick flue?

cehs
09-30-2011, 09:32 PM
5" flue, double wall from basement through the middle of the house all the way to the roof (2 story).
Furnace has a 4" going into the 5" along with a 3" from the gas water heater.
I have NOT measured the flue temp.
.

Kenoo8
10-03-2011, 09:21 AM
I would measure the flue temp, the furnace is induced draft correct, since the main flue is 5" I am not sure if the standing pilot in the water heater will produce enought heat to keep it from condensating. In a cold climate area I had to insulate the doulble wall flue to stop this problem . Mainly in the basement.