fixitguy
09-27-2011, 12:18 AM
4TWX3036A1000A
So I went on a "not working very well heat pump" call
Suct was 45 high side was 200psi OAT 70 degrees.
Liquid line was 75, chart says HIGH side should be 250 so I
add 4 lbs to get to 250 PSI.. [TXV indoor]
low side got up to 55-60
This is 410 so should have been like 105-110 psi as I recall.
Course I checked for airflow b4 hanging the gauges on the outdoor unit.
So after added the 410 I visually checked the indoor TXV and the feeder tubesand the bottom 4 elbows were frosted..
TXV is bad.. Does that diagnosis seem correct to you wise old pros??
But I couldnt find the sheet for the defrost board and it was flashing
[1 led] either a fast 3 or 4.
Thanks a lot in advance.
Portland,OR
So I went on a "not working very well heat pump" call
Suct was 45 high side was 200psi OAT 70 degrees.
Liquid line was 75, chart says HIGH side should be 250 so I
add 4 lbs to get to 250 PSI.. [TXV indoor]
low side got up to 55-60
This is 410 so should have been like 105-110 psi as I recall.
Course I checked for airflow b4 hanging the gauges on the outdoor unit.
So after added the 410 I visually checked the indoor TXV and the feeder tubesand the bottom 4 elbows were frosted..
TXV is bad.. Does that diagnosis seem correct to you wise old pros??
But I couldnt find the sheet for the defrost board and it was flashing
[1 led] either a fast 3 or 4.
Thanks a lot in advance.
Portland,OR