PDA

View Full Version : Ventilation Rqmt in Mechanical Room



BC Eagle
09-13-2011, 08:41 PM
Hello pros,
Appreciate any advice you offer. We are remodeling a basement in our 10 year old home by adding a bedroom to an open space that includes a furnace and water heater on one end. The furnace is a HE gas Trane unit with intake and combustion air vented outside, that was added last year by the previous owners. The 80k BTU gas water heater has an electric blower on top, but I believe the combustion air comes from the room. This new downsized mechanical room is about 9' x 11.5' with a 9' ceiling. There was conditioned air delivered into the room before the remodel started, but that has now been sealed.

Today our contractor said he needed to add an air passage vent from one of the adjacent living spaces to the mechanical room. Do we really need to do this? Can adding a replacement conditioned air vent meet this need?
Brian

beshvac
09-13-2011, 09:05 PM
No, you need the properly sized pass thru grills (ceiling and floor) to communicate to a large enough space to provide combustion air.

beenthere
09-13-2011, 09:14 PM
An 80,000 BTU gas fired appliance needs a free air volume of 4,000 cubic foot. So yes, you need to have combustion air added to that room.

BC Eagle
09-13-2011, 10:05 PM
I was afraid that would be the answer. We'll make it work. Thanks for the help!
Brian

tedkidd
09-13-2011, 11:41 PM
Kick the low efficiency pig to the curb. Install a 98% efficient sealed combustion on demand water heater and you can leave the room alone.

second opinion
09-14-2011, 09:18 AM
Make sure they follow IFGC section 304 and IMC section 702.3,---702.3.1 and 702.3.2

also IFGC section 303

motoguy128
09-14-2011, 10:46 AM
Kick the low efficiency pig to the curb. Install a 98% efficient sealed combustion on demand water heater and you can leave the room alone.

+1. If the hot water heater is the original builder grade unit, it's worth replacing. I'd get a HE unit as mentioned above. One AO Smith unit has enough output capacity that it can provide almost continous hot water almost like a on demand system. I plan to install one of those in the next few years to get my flue out of my chimney... or rather to stop using my 86 y/o brick probably unlined chimney as a flue.

Gross
10-09-2011, 02:52 AM
Hello pros,
Appreciate any advice you offer. We are remodeling a basement in our 10 year old home by adding a bedroom to an open space that includes a furnace and water heater on one end. The furnace is a HE gas Trane unit with intake and combustion air vented outside, that was added last year by the previous owners. The 80k BTU gas water heater has an electric blower on top, but I believe the combustion air comes from the room. This new downsized mechanical room is about 9' x 11.5' with a 9' ceiling. There was conditioned air delivered into the room before the remodel started, but that has now been sealed.

Today our contractor said he needed to add an air passage vent from one of the adjacent living spaces to the mechanical room. Do we really need to do this? Can adding a replacement conditioned air vent meet this need?
Brian

omg yes! its the only sure way to do it. cutting a hole in a wall doesnt mean air will go into that room.

dandyme
10-09-2011, 07:06 AM
No, you need the properly sized pass thru grills (ceiling and floor) to communicate to a large enough space to provide combustion air.



are you suggesting taking ventilation air from inside the structure/living ares?




An 80,000 BTU gas fired appliance needs a free air volume of 4,000 cubic foot. So yes, you need to have combustion air added to that room.

even a 90+ 2-pipe?

vangoghsear
10-09-2011, 08:02 AM
Isn't it true that transfer air can be through openings or mechanically induced through a fan? The problem I see with the A/C vent is that there is no guarantee that the unit will be running to bring in air when the gas water heater is firing.

Couldn't a dedicated supply fan be used to blow air into the room, either a constantly running or interlocked with the water heater, as an option?

boilerman856
10-09-2011, 08:12 AM
You are not allowed ato put a non sealed combustion gas water heater in a bedroom, I would think you shouldn't take combustion air from that room through grilles either. Better call the code enforcement officer or fire chief on thar one first

jpsmith1cm
10-09-2011, 08:24 AM
You are not allowed ato put a non sealed combustion gas water heater in a bedroom, I would think you shouldn't take combustion air from that room through grilles either. Better call the code enforcement officer or fire chief on thar one first

Boilerman856,

Read and follow AOP forum rules.

You should apply for Professional Membership.

genduct
10-11-2011, 07:46 AM
Boilerman856,

Read and follow AOP forum rules.

You should apply for Professional Membership.

Although there is a good reason to have and follow rules, even if they are newly instituted, I would like to point out that what boilerman said, in no uncertain terms, is what secondopinion referenced in his post.
Clearly boilerman has been very forthright and correct in warning the OP with his remarks and is right in doing so in a potentially dangerous situation.

So I think if your post could have begun with a thank you, agreed with him and then invite him to apply. The OP might have gotten the idea that boilerman's concerns were not valid.
NO GAS APPLIANCES IN SLEEPING AREAS ALLOWED
We would like to see the occupants wake up in the morning

boilerman856
10-11-2011, 09:43 AM
Thank you genduct. I am fairly new to this world of forums and apparently keep stepping on someones toes. I am not sure what rule i broke this time but i am open to help anytime. I am having printer trouble at home so applying for pro has been impossible lately. When it is fixed i will certainlyt do so. Thanks again

jpsmith1cm
10-11-2011, 12:28 PM
I try not to pass judgement on anyones posts unless I find the advice wildly inappropriate.

You posted advice in AOP forums without following the rules.

At this point, the quality of your advice is immaterial. You are not a Professional Member * of this site and thus are not permitted by site rules to post any advice in the AOP forums.

I invite you to apply for professional membership, then apply for the AOP *.

surenuff
10-11-2011, 02:06 PM
You are not allowed ato put a non sealed combustion gas water heater in a bedroom, I would think you shouldn't take combustion air from that room through grilles either. Better call the code enforcement officer or fire chief on thar one first

What he said !!!! Now it is legal.

genduct
10-11-2011, 07:34 PM
I try not to pass judgement on anyones posts unless I find the advice wildly inappropriate.

You posted advice in AOP forums without following the rules.

At this point, the quality of your advice is immaterial. You are not a Professional Member * of this site and thus are not permitted by site rules to post any advice in the AOP forums.

I invite you to apply for professional membership, then apply for the AOP *.

It kinda sounded like you were criticizing the boilerman for my remarks. I don't think that is true but in case it is please don't think badly of him for my remarks.
As I said, I understand this new approach is going to take some getting used to, and your job is to ermind us, but I thought it would be helpful to share the idea that your taking issue with the boilerman's status could have allowed the OP to ignore some sound advice, SO in this effort to enforce the rules would it have been too much for you to respond to boilermans good advice along with your encouragement to apply for PRO Status?

Just wondering is all, Mike

hvacvegas
10-11-2011, 09:04 PM
Get a direct vent water heater.

problem solved.

Doesn't even have to be an instant water heater.
State Select makes a 2 pipe water heater, along with the AO smith vortex.

jpsmith1cm
10-11-2011, 10:08 PM
It kinda sounded like you were criticizing the boilerman for my remarks. I don't think that is true but in case it is please don't think badly of him for my remarks.
As I said, I understand this new approach is going to take some getting used to, and your job is to ermind us, but I thought it would be helpful to share the idea that your taking issue with the boilerman's status could have allowed the OP to ignore some sound advice, SO in this effort to enforce the rules would it have been too much for you to respond to boilermans good advice along with your encouragement to apply for PRO Status?

Just wondering is all, Mike


My point stands, The purpose of these forums is for qualified and vetted Professionals to offer advice to homeowners in need.

Regardless of the quality of his advice (and I don't deal with fuel burning equipment within living spaces and cannot accurately comment on what is and is not 'code', by the way), it really makes no difference.

There are rules and the rules are in place for a reason.

genduct
10-12-2011, 08:49 AM
No need to call the Police!