PDA

View Full Version : CARRIER 38AR INFO



mrhvacmechanic
12-16-2005, 07:37 PM
Can anyone provide me with the cut in and cut out factory settings on the high, low, and fan cycling pressure swiches on this condensor???????????

Carrier Air Cooled M#38ARDO16501
Has two compressors w/two cond fans. Hav no access to caralogs until Monday. Need info for tomorrow morning.

jrbenny
12-16-2005, 08:33 PM
http://www.xpedio.carrier.com/idc/groups/public/documents/techlit/38a-18si.pdf

Cut and paste:

The no. 2 fan cycles in response to changes in liquid pressure. The switch cycles the fan off at 160 ± 10 psig (1103 ± 69 kPa) as pressure decreases, and cycles it back on at 255 ± 10 psig (1758 ± 69 kPa).


Pressurestat (psig)
High Cutout 426 ± 7
Cut-in 320 ± 20
Low Cutout 27 ± 4
Cut-in 67 ± 7

mrhvacmechanic
12-16-2005, 08:35 PM
Thanks JR!!!