View Full Version : Basic Question, I feel dumb asking
coolerguy
09-03-2011, 08:21 AM
Had a call on an old Carrier RTU about 2 weeks ago, don't know the model # its about 5 ton, built about 1983. Problem was a welded contactor, no big deal, changed it out all checked out. I installed a 30 amp contactor compressor running around 15 amps RLA. Didn't think much about it, this week I get a call, find the contactor I installed totally trashed, the bar and spring between the points laying in the bottom of the panel and points melted to the point of nothing left. The other pole was fine (2 pole contactor), this time I installed a 40 amp square D, mega ohm compressor, its good, power is clean (least while I was there). Thermostat is a digital Honeywell that has a time delay, so I know noone is jamming it off and on. 24 volts coming back on Y1 and 24v @ coil. It does has A CLO card that works, economizer is bypassed because owner does not want to spend the money to fix it, so we know the economizer has no control over compressor, for what its worth..Suggestions please ?
dandyme
09-03-2011, 08:43 AM
HP,AC, or gas pak?
30a seems kinda light
what was start up A?
grayghost
09-03-2011, 09:16 AM
single or three phase ? What did disconnect forks look like ? Is time delay the last device before contactor coil?
HJ Controls
09-03-2011, 10:00 AM
did you check start and run amps, wouldn't hurt to make sure your not flooding and check wiring from contactor to compressor.
ScottBeck
09-03-2011, 03:51 PM
Does it have a saftey board on it? The low and high presure switch and one leg of the compressor goes through a current sensor. I have seen those boards short cycle power the the contactor. Its hard to catch unless you are there when it happens
Sun Dog
09-04-2011, 02:42 AM
One pole fried...., other not....Sounds like Scott may have a likely cause-don't think I've seen one quite like that....
XcelTech
09-04-2011, 03:15 AM
I have been getting a rash of bad contactors recently. They run for a week or two then the coils get weak and start chattering. I am actually replacing one on Tuesday. I got two from Trane on brand new DX systems and one from Baker Dist. (all three replaced at no extra cost or hassle Thank you to both companies) all this month. Might be a common coil maker being used by several contactor companies. Copper is getting expensive you know. :)
pdrake65
09-04-2011, 08:01 AM
Possilbe bad contactor coil as previously stated. I might be concerned about installing a 40 amp where a 30 amp ran for years without issue. Could cause more damage than just a contactor.:.02:
mcewans
09-04-2011, 10:39 AM
Possilbe bad contactor coil as previously stated. I might be concerned about installing a 40 amp where a 30 amp ran for years without issue. Could cause more damage than just a contactor.:.02:
This should not be an issue as long as you have the proper sized circuit breaker/fuse installed upstream of the contactor.
pdrake65
09-04-2011, 11:08 AM
This should not be an issue as long as you have the proper sized circuit breaker/fuse installed upstream of the contactor.
Maybe I should clarify my line of thinking with a question to Coolerguy. Did you put a 40 amp in because you didn't have a 30 amp or did you feel that the unit was drawing more amps than the 30 amp could handle and that was the cause for the meltdown?
Have you tested the CLO?
Pull low voltage off term 3. CLO should trip. Check by measuring 24v across term X and term 1. Then put wire back on term 3 and check voltage at term 3 and term 1.
In the past I installed a voltage recorder
boilerman856
09-04-2011, 08:16 PM
If it is 3phase wouldnt a voltage imbalance cause this? Just an idea.
rucomfy101
09-05-2011, 07:28 AM
A couple suggestions:
1. Check compressor winding resistances and compare to known good
2. Intermittent voltage drop in circuit
3. Saw something like this before, intermittent logic fault in CLO board would cause compressor contactor to chatter severely. Parts laying in compartment as you stated would appear that the chattering got worse than the one I worked on. It was not a pretty sight but I did see it occur. Replaced the CLO and contactor OEM (94 rated amp)
all good. Sounds like a 48DJ, with the 06 semi on the filter access corner side.
Try a new CLO when you replace the CC and double check the OEM recommendation for RLA.
coolerguy
09-05-2011, 08:49 AM
Maybe I should clarify my line of thinking with a question to Coolerguy. Did you put a 40 amp in because you didn't have a 30 amp or did you feel that the unit was drawing more amps than the 30 amp could handle and that was the cause for the meltdown?
I wanted to install a higher quality (if thats even possible) all I had in a square d was a 40 amp..it only runs about 15 amps +/-, and is properly fused.
coolerguy
09-05-2011, 08:51 AM
single or three phase ? What did disconnect forks look like ? Is time delay the last device before contactor coil?
It is a 3 phase, however as you know, most carriers only break 2 legs and the 3rd is wired hot. The only time delay, is the thermostat, nothing else is present after that. Knives looked good in disconnect as well as wiring to terminals, no burnt wires..
coolerguy
09-05-2011, 08:53 AM
Have you tested the CLO?
Pull low voltage off term 3. CLO should trip. Check by measuring 24v across term X and term 1. Then put wire back on term 3 and check voltage at term 3 and term 1.
Yes I have tested it, worked properly while I was there.
coolerguy
09-05-2011, 08:57 AM
A couple suggestions:
1. Check compressor winding resistances and compare to known good
2. Intermittent voltage drop in circuit
3. Saw something like this before, intermittent logic fault in CLO board would cause compressor contactor to chatter severely. Parts laying in compartment as you stated would appear that the chattering got worse than the one I worked on. It was not a pretty sight but I did see it occur. Replaced the CLO and contactor OEM (94 rated amp)
all good. Sounds like a 48DJ, with the 06 semi on the filter access corner side.
Try a new CLO when you replace the CC and double check the OEM recommendation for RLA.
Compressor did check out ok with mega ohm, voltage ok while im there, thats not to say something doesnt change while im not there. Hmm you got me thinking... If it happens again I think I will change CLO.
coolerguy
09-05-2011, 09:02 AM
HP,AC, or gas pak?
30a seems kinda light
what was start up A?
It is gas heat and a/c. LRA.. be honest I overlooked.. my bad.. RLA was 20, actual running 15.
coolerguy
09-05-2011, 09:05 AM
I have been getting a rash of bad contactors recently. They run for a week or two then the coils get weak and start chattering. I am actually replacing one on Tuesday. I got two from Trane on brand new DX systems and one from Baker Dist. (all three replaced at no extra cost or hassle Thank you to both companies) all this month. Might be a common coil maker being used by several contactor companies. Copper is getting expensive you know. :)
I did think of this too. I just bought my stock about a month ago, time will tell. Although customers dont want to hear that.. Always the techs fault.:angel: