11-15-2005, 11:02 PM
Hi
Recently installed a Venmar HRV Solo 2.0 and connected the HRV's intergrated interlock relay to furnaces R&G terminal block (Amana Air Command 90 gas). The HRV does activate the blower motor as it is supposed to when the HRV runs.
The Problem is that when the HRV is running and energizing these terminals, and the thermostat calls for heat the furnace will not run. (Thermostat set in auto fan mode).
Howerver, If i set the thermostat fan mode from <auto> to <on>(continuous) the HRV will run nomally and the furnace will run normally if called and slows the blower speed automatically to coincide with the preset heat blower speed setting.
The thermostat is an aprilaire 8334 1 heat/1 cool digital.
Would like to remedy so that blower motor runs when hrv is operating (not continuous), but obivously need to have heat when the thermostat calls.
any help would be appreciated, dont know if this is a furnace or thermostat issue.
thanks!
Recently installed a Venmar HRV Solo 2.0 and connected the HRV's intergrated interlock relay to furnaces R&G terminal block (Amana Air Command 90 gas). The HRV does activate the blower motor as it is supposed to when the HRV runs.
The Problem is that when the HRV is running and energizing these terminals, and the thermostat calls for heat the furnace will not run. (Thermostat set in auto fan mode).
Howerver, If i set the thermostat fan mode from <auto> to <on>(continuous) the HRV will run nomally and the furnace will run normally if called and slows the blower speed automatically to coincide with the preset heat blower speed setting.
The thermostat is an aprilaire 8334 1 heat/1 cool digital.
Would like to remedy so that blower motor runs when hrv is operating (not continuous), but obivously need to have heat when the thermostat calls.
any help would be appreciated, dont know if this is a furnace or thermostat issue.
thanks!