PDA

View Full Version : Digi-cools low side wont go over 200 psig



rogerk
07-16-2011, 12:15 AM
Will they ever make a set of Digi-cools that will allow the low side to read over 199 psig? Why cant they use the same sensor for the low side that is used for the high side?

bigmanmikey
07-16-2011, 12:33 AM
think it has something to do with the low side reading tenths... like 125.5 etc.. an dont think theres any ref that runover 199 psig on the low side :)

acguytx
07-16-2011, 07:48 AM
think it has something to do with the low side reading tenths... like 125.5 etc.. an dont think theres any ref that runover 199 psig on the low side :)

except when you are trying to leak test with nitro 250-500 psi , nice to be able to stop the blinking :P :.02:

bigmanmikey
07-16-2011, 09:05 AM
there was another posting about testing with nitro an what press seams like most guys around the 100 mark..

rogerk
07-16-2011, 09:09 PM
there was another posting about testing with nitro an what press seams like most guys around the 100 mark..

I like 250 myself. I did an install yesterday where it held at 150 psig but I said give me more gas at which point a small pinhole leak blew at the evap suction line I brazed. Would it have blown open at 100? Glad I went up to 250.

acguytx
07-18-2011, 07:19 AM
I like 250 myself. I did an install yesterday where it held at 150 psig but I said give me more gas at which point a small pinhole leak blew at the evap suction line I brazed. Would it have blown open at 100? Glad I went up to 250.

ditto if a system has the potential to run at pressures of 250(22)-450(410) then i cant see why you wouldnt test at those pressures? Nitro is cheap, fast and not hard to put in and take out of a system, plus gives me an extra flush on these conversions.

to each their own but i test higher..:cheers:

itsiceman
07-18-2011, 10:37 PM
Why cant they use the same sensor for the low side that is used for the high side?They are both rated at .5% FS so if the full scale (FS) is lower the more accurate the sensor is reading. Plenty of guys like the accuracy the way it is. It is very accurate and I believe that accuracy is over the entire operating temp not just at room temp where some other gauges are listed.

Digi-Cool lists
Proof pressure: Tolerable pressure without internal damage
Low side: 600psia
High side: 1500psia

and Burst pressure: Tolerable pressure with out loss of seal
Low side: 2000 psia
High side: 5000 psia

A piping system should be pressure tested for strength and tightness.
You normally run the pressure up for a strength then test for tightness at a lower pressure over time.
Personally I use only the high side for any strength testing.
If you are testing for tightness you are much better off with a gauge with the most accuracy you can get like the low side of a Digi-Cool gauge :.02:

itsiceman
07-18-2011, 10:55 PM
Here is a good article that was in the RSES Journal that Jim Bergmann wrote on pressure testing.

http://www.rses.org/assets/rses_journal/0710_Leak.pdf