10-06-2005, 07:46 AM
I have a Carrier 30GB Flow-Tronic, which is still tripping on a Code 51 compressor failure.I jumped the HG and HP switch, and changed the cpcs board.
The only thing remaining according to the manual is current to ground, but the compressor is 3 months old and amping out OK. So, maybe I could dissconnect the toroid wires to the cpcs? But, Carrier says not to. I ran out of time and have to return.
I think the problem is the microprocessor board; it's the original from 1988.
The only thing remaining according to the manual is current to ground, but the compressor is 3 months old and amping out OK. So, maybe I could dissconnect the toroid wires to the cpcs? But, Carrier says not to. I ran out of time and have to return.
I think the problem is the microprocessor board; it's the original from 1988.