what is the charging calculation formula used when 25 feet pre-charged line set R-22 is extended to 50 feet ?
how much more refrigerant needed to the additional 25 feet line set without refrigerant in it ?
jpsmith1cm
06-18-2011, 09:39 AM
What type of metering device?
What are the indoor conditions, outdoor conditions?
Type of refrigerant doesn't matter.
What type of metering device?
What are the indoor conditions, outdoor conditions?
Type of refrigerant doesn't matter.
Not to mention what is the line set size!
darctangent
06-18-2011, 10:16 AM
Sorry, panaboro.
No DIY help to non pro members.
Read site rules and apply for pro status if you qualify.
panaboro
06-18-2011, 01:38 PM
what is the charging calculation formula used when 25 feet pre-charged line set R-22 is extended to 50 feet ?
how much more refrigerant needed to the additional 25 feet line set without refrigerant in it ?
3/8 liquid and 7/8 suction with TXV. there is no mention indoor/outdoor condition. but i guest will be standard design temperature 95*outdoor and 75* indoor 50% RH
I had a test question a month ago that i can't find the answer in my book.
thanks
panaboro
06-18-2011, 01:40 PM
I want to find the answer for a test question i had a months ago.
i can do subcooling or superheat but its a test.
thanks
jpsmith1cm
06-18-2011, 01:41 PM
I'm sorry, I misread the question.
This is actually a queston regarding the volume added to the lineset and the density of the refrigerant.
The BEST way to correctly charge a unit is to use superheat or subcooling depending on the metering device.