Need some help here!

just changed a residential copeland cr32k6 and the compressor continues to shut down on internal protector. Everything on the system checks out, the compressor is shutting down at HS 200psig and suction of 60psig (I was still adding gas to the low side when it shut down.) Ambient temp is about 80degrees.

Measured current (when running) at 8amps across both compressor leads. Voltage is good and constant; 122volts both legs. Capacitor is good and new. I did not change the contactor, but exisiting one checks good.

It's a simple system, no other HP or LP protection just a compressor, fan, starter and capacitor, but the compressor will not stay running.

The compressor I was replacing was doing the same thing and I determined it was internal overload failure. I cleaned the system up with deep vacuum purged with nitrogen and vacuumed again. Installed a sporlan c-163 drier and I'm not having head pressure problems.

Any hints for something I've missed would be appreciated.

foglifter
06-12-2011, 07:58 PM
VTP99 asked about other start components.

Answer: There aren't any other components. It's a Heil condensor unit consisting entirely of the starter/contactor, capacitor, fan and compressor that's it. The replacement compressor going in is identical to the one coming out - right down to the not running part. Wiring and system diagram is spot on with Copeland electrical manual.

Dr.phil
06-13-2011, 12:08 PM
You sure it's off on internal? What is your superheat? How long until it shuts down? There has to be enough refrigerant to cool the compressor.