View Full Version : Replacing A coil with N
jvrba1
06-10-2011, 08:31 AM
Hi I'm looking for some advice.
I have a 3 ton Carrier Condenser (Straight A/C) with a 3 ton Whirlpool air handler. The A coil had leaks so it was replaced with a "N" coil. The original unit had a piston the new coil has a TXV. I'm having issues with the coil freezing up. The bulb is securely mounted (factory). The unit was charged per manufaturer recommendations. (Super heat). Am I missing something?
92 degrees outside 86 RH. Indoor WB 75.5, 29 degree superheat.
Any clues?
jvrba1
06-10-2011, 08:32 AM
The new N coil was what Carrier Mid-atlantic recommended replacing the A coil with.
beshvac
06-10-2011, 08:46 AM
1. You don't charge a txv by superheat
2. You don't have matching equipment
3. What are the model numbers of the carrier and whirlpool?
jvrba1
06-10-2011, 09:04 AM
Condenser - Carrier 38EN0363205M
Air handler - Whirlpool 4386CE41397
New N Coil - CNRVU3617ATA
I would say that the biggest thing missed is how it was charged. Not sure if you could get an accurate wiegh-n due to non matched components. Only option is subcool charge.
HAP
darctangent
06-10-2011, 09:33 AM
Correction -
I have read your past posts.
Either you are a bad as average tech that is afraid to come out and admit it or you are a meddlesome DIY.
You know site rules prohibit DIY.
Cease please.
I won't help any longer.
jvrba1
06-10-2011, 09:38 AM
TXV is fixed no adjustment.
Could be the air flow, unit is very clean for it's age. filter is brand new.
A member on the site told me the unit should not be charged via super heat now that a TXV is in the equation. How should a TXV unit be charged? Sub cooling?
beshvac
06-10-2011, 09:42 AM
Who installed that coil.....
and was it one of the "counter guys" that only know what their computer tells them (and the computer would never tell them that was a matchup) that told you it would work?
darctangent
06-10-2011, 09:49 AM
READ PAST POSTS BY OP
POSTER IS DIY
jvrba1
06-10-2011, 09:57 AM
Yes it was a counter guy who sold the coil.
Who is OP and where can I find the posts?
beshvac
06-10-2011, 10:03 AM
Well the counter guy can now successfully match a new condenser to the oversized coil (as long as the current compressor doesn't burn-out and fill the system with acid and/or they have any R22 condensers available) :cliff:
darctangent
06-10-2011, 10:05 AM
Well the counter guy can now successfully match a new condenser to the oversized coil (as long as the current compressor doesn't burn-out and fill the system with acid and/or they have any R22 condensers available) :cliff:
I'd recommend increasing the lineset size to 1/2" and 1 1/8 that'll fix it.
jvrba1
06-10-2011, 10:23 AM
How do I know that increasing the line set will not create another problem?
The line set is 3/8" and 3/4" what will increasing the sizes do for me?
Tell me what's going on with the refrigerant? Why is the coil now oversized?
3 ton Air handler with a 3 ton evaporator coil and condenser. What Am I missing?
woody19
06-10-2011, 10:26 AM
I'd recommend increasing the lineset size to 1/2" and 1 1/8 that'll fix it.
LOL you're bad
beshvac
06-10-2011, 10:35 AM
How do I know that increasing the line set will not create another problem?
The line set is 3/8" and 3/4" what will increasing the sizes do for me?
Tell me what's going on with the refrigerant? Why is the coil now oversized?
3 ton Air handler with a 3 ton evaporator coil and condenser. What Am I missing?
You have an 8 seer condenser from the 80's......
You now have a coil from 2011 made to work with modern 13-20 SEER condensers........
:worthless:
catmanacman
06-10-2011, 07:48 PM
38 degree superheat on a txv coil time to find a installer that has a clue
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.