Ctl-fool
06-08-2011, 04:49 PM
Here was an interesting situation I ran into recently:
ALC module (ME Controller) using its 0-10vdc analog output to another ALC (OEM I/O Zone controller) analog input set at 0-5v at In1. Both controllers powered off of same transformer. As soon as controllers are powered up, transformer ckt breaker trips. Tech on site reads ~12vdc (and ac) between input wire and earth ground. If ao wire not hooked to AI, no trip.
I'd shoot for wire mixup as a guess...Ive hooked ao's to ai's before and never seen this (especially if both controllers using same xfr).
Any other guesses?
ALC module (ME Controller) using its 0-10vdc analog output to another ALC (OEM I/O Zone controller) analog input set at 0-5v at In1. Both controllers powered off of same transformer. As soon as controllers are powered up, transformer ckt breaker trips. Tech on site reads ~12vdc (and ac) between input wire and earth ground. If ao wire not hooked to AI, no trip.
I'd shoot for wire mixup as a guess...Ive hooked ao's to ai's before and never seen this (especially if both controllers using same xfr).
Any other guesses?