PDA

View Full Version : Need Novar transducer replacement



incontrol
09-11-2005, 04:35 PM
I've got a Novar IMP1010 pneumatic transdure that needs replacing. I believe it takes a pulsed contact and converts it to PSI. Any parts suggestions? I've found this but am not sure of the time settings.

http://www.kele.com/cgi-bin/navigate.cgi?cat=Models%20UCP-522,%20%20UCP-622&js=setuser

[Edited by incontrol on 09-11-2005 at 04:39 PM]

dapper
09-11-2005, 06:18 PM
I am assuming that you are looking at the UCP622 control. As is stated, the time base is DIP switch selectable. You should be able to match this to your existing controller. The Novar panels that I have seen around here actually use the Kele controller. They are/were manufactured by Day Automation. Check your existing controller. If it is the Day controller then let me know. I often work with one of their service techs and can get you any info that you need.

incontrol
09-12-2005, 10:48 PM
I have no idea what the pulse from the novar is to set it up.

dapper
09-13-2005, 05:27 AM
If the boards being used are the old Kele cards look in the upperleft corner. There will be a set of 2 rows of pins. There should be a little plastic jumper across one pair of pins. On the board alongside the pins it should tell you what the pulse rate is. Hope this helps

jciengineer
09-15-2005, 11:59 AM
Hey bud, hopefully I can steer you in the right direction. Kele is great don't get me wrong but in this situation I would go else where. Try one of the following, i suggest the first one:

1 veris - http://www.veris.com

2 ACT - http://www.act-solutions.com

GOOD LUCK :)

letmedance
07-17-2007, 05:09 PM
We have a Gaggle of the IMP-1010 along with other Novar components.

Drop me an email

John

rolo
07-17-2007, 09:22 PM
this post is 2 years old wake up novar fails a lot

orion242
07-17-2007, 09:30 PM
Pretty sure you will need to reprogram the system for PWM output to use another transducer. The IMP is using what Novar calls "closed loop multiplexed PWM".

Your signals currently should be

Steady off = both valves closed
Pulsed = A valve only, increasing output pressure
Steady on = B valve only, exhausting branch pressure

This screw ball signal is something I have never seen on another transducer. If you have ESS, switch over the output type to analog out - PWM and use a UCP from Kele or whatever.

Novar PWM has a time base of .59-2.59 secs

Or save yourself the headache and get another IMP, which may be possible this time. Not too likely down the road.

twisted pair
07-17-2007, 09:42 PM
Right on Orion. You saved me some typing. I found that information out the hard way on a retrofit where I planned on reusing 110 of those pneumatic transducers, and ultimately had to replace them.

I thought Mamac Systems may have made that for Novar.

Rolo is a Novar expert now!!!!!!!!!

amsolo
07-18-2007, 06:41 AM
he's what I got;

Novar time pulse
4ma = .59 sec
20ma = 2.93 sec

Mikeylikesit
01-15-2008, 03:05 PM
I have IMP1010's thruout my facility, and they have begun to fail. I am told that this part is no longer available.

Our NOVAR rep came out and installed a "KELE" electric/pneumatic transducer, model # UCP-322.

the only downside is that this controller requires 2 outputs from the IOM, where as the IMP1010 only needed 1.

seems to be doing the job!

orion242
01-15-2008, 07:33 PM
Well the UPC-522 is what we typically would use. It only needs a single output to get the job done.

http://www.kele.com/olcat/OT8/ucp-522_ucp-622.pdf

Page 3 PWM wiring.

Mikeylikesit
01-15-2008, 08:02 PM
Well the UPC-522 is what we typically would use. It only needs a single output to get the job done.

http://www.kele.com/olcat/OT8/ucp-522_ucp-622.pdf

Page 3 PWM wiring.

thanks, good info there!

I will pass that along, however, most all of my IOM's have unused outputs. Wonder what the price difference is between the 2.

orion242
01-15-2008, 08:29 PM
>Wonder what the price difference is between the 2.

About double.

Still a whole hell of alot cheaper than another IOM when you run out of outputs.

Mikeylikesit
01-16-2008, 09:48 AM
>Wonder what the price difference is between the 2.

About double.

Still a whole hell of alot cheaper than another IOM when you run out of outputs.

man, you're not kidding there! We just bought an IOM2 to have as a "spare".....$$$$$ but if one fails, and there are no replacements available, it is cheap insurance.


Well, I never should have posted. I came in this morning to have no heat in my 500 building, and you know what the culprit is! Yep, that darn IMP.
I will have to try to get a 533.