I am working on a Hussman Rack that continues to go into alarm for proof failure and i cannot find any literature on it... Any feedback??

keviekev70
04-30-2011, 10:41 PM
how do you know that?

snowboard106200
04-30-2011, 10:49 PM
Occurrence Date
Type
Source-Directory
Source-Site
Source-Control System
Source-Unit
Source-Application Type
Source-Application Instance
Source-Point
Priority
Advisory Message
Source Type
Advisory Limit
Property Value
Received Date

4/29/11 6:41:00 PM
Fail
WinCo Foods
102 Lacey
E2
CX-400 3: BMS #102
Enhanced Suction
RKE A/C R404A
STAGE OUT1
20
Proof failure Occurred
Device


4/30/11 6:53:09 AM (3)
From the Emerson E2 Controller

jpsmith1cm
04-30-2011, 10:53 PM
Well, the short version is that, for that time, the compressor's run state doesn't match it's required state.

Why takes a professional and experienced technician to determine.

snowboard106200
04-30-2011, 11:06 PM
Thanks Mr. Smith.....

emcontrols
04-30-2011, 11:57 PM
As JP said, there was a call for the compressor but no amp draw was detected. It could be several different things causing the problem. Is this your first rack system and emerson CPC system??

Need a lot more info! What kind of compressors scroll (digital) or semi hermetic. What kind of current switch (fixed or adj), what is the amp range of CT, what is the RLA of the compressor, How much diagnostics have you done thus far, need to know history. Is this occuring every 5 minutes, once a month, first time ever, how old is the rack? etc....

pherman
05-01-2011, 12:59 AM
is the proof a digital input from an aux. switch on the contactor? does the compressor run ever? does the contactor even pull in?

jpsmith1cm
05-01-2011, 07:43 AM
Thanks Mr. Smith.....

You DO realize that Rack systems are custom made and nearly unique to their application.

Without more details, we really can't help you much.