04-25-2011, 08:19 PM
hey guys/gals...i new to this site but was told u could get good info here

So my question is.. I have a freezer that is on a wastwater system to cool the condser...and im wonder if there is a stander or rule of thumb on calculating the correct HP. the control valve has been messed with and im not sure if its being stavered for water....

griffic1
05-21-2011, 10:27 PM
If you have a water cooled condenser then you need to look at inlet and outlet water temps there should be about a 10 degree split.

bc guy
05-22-2011, 05:43 PM
hey guys/gals...i new to this site but was told u could get good info here

So my question is.. I have a freezer that is on a wastwater system to cool the condser...and im wonder if there is a stander or rule of thumb on calculating the correct HP. the control valve has been messed with and im not sure if its being stavered for water....

I usually look for 105F sat cond. temp (converted from head pressure for type of refrigerant)

keviekev70
05-22-2011, 06:00 PM
If you have a water cooled condenser then you need to look at inlet and outlet water temps there should be about a 10 degree split.

If that condenser is fouled, @10* something would be tripping out.

Also the city water would be around 50*,and as your calculation you would have 60* (10*TD) on the outlet, what would your high side pressure be? And would it be high enough to create the appropriate pressure differential across the metering device with the proper refrigerant charge?

keviekev70
05-22-2011, 06:02 PM
I usually look for 105F sat cond. temp (converted from head pressure for type of refrigerant)