View Full Version : VAVII boxes default to 10" after sync?



reissman
04-21-2011, 12:56 PM
Kinda stumped here. I have an LNS controlled database with Care 8.02. After I synchronized the database the balancer noticed all the boxes were defaulted to 10"? If I look at them with the plug in they are set to what I programmed them for, but if you look at them through rapid balance they are all the same 10"? Tac told me to ensure I checked the box "enable care controlled flow parameters for Honeywell VAV2 devices" on the lon tab and resync. I did that and they are still wrong. I can change them in rapid balance and it takes, but the next time its synched it will be wrong.

Any suggestions?

blindhog
04-21-2011, 02:15 PM
Any changes you make with RapidBalance or from your SymmetrE/EBI need to be uploaded to CARE before you synch.

choosewisely
04-21-2011, 02:17 PM
In the same window where the LNS Controlled checkbox is, there is a checkbox under it that says "enable CARE Controller flow parameters for Honeywell VAV2 devices.
It is supposed to be checked