MUNC
04-15-2011, 01:52 PM
Hey guys need a little in put about a Benchmark 2.0 boiler. 16955 hours on it. 6-7 years old. I think never setup from install. NOTE three others tuned ok but this one gives me fits. At 40% fire rate flue gases spot on @ 16% fire same,spot on. Then when you take it to 100% you can't get past 80% fire rate and the thing starts to sputter and pop out the flue. My co goes above 10,00ppm. O2 drops to near zero, cant get gas pressure to the spec of 7.0"wc. all other boilers on same gas line all no problem. Removed combustion air hose to see if something was resticting air= same. pulled burner and saw that some of the "swirl turbulator" fins where bent over from getting too hot. reassembled after cleaning burner and same thing. is there a spec for an air side pressure drop across these exchangers? and is there a good place to take readings on the air side? All 4 boilers got the seasonal kits so flame rods and igniters new. Could low gas be caused by the combustion back firing which is a product of a partialy plugged x-changer? ( O.K.@ 16 & 40%) Any way of visiualy inspecting lower portion of air side of x-changer short of pulling the whole thing out and and tearing it down? If this thing was a car i'd say the timing chain has jumped it pops that bad. Any ideas will be greatly appreciated thanks MUNC