07-12-2005, 05:24 PM
went to service a refrigerator today thought it would be simple,but thats life.I could here the start relay 0pening and closing with the compressor making a hummmmm.and upon that i checked the compacitor for the rating of Uf which was correct,then voltage at relay which was correct also.then ohm out the compressor my reading are 7-5-3 from start to commond, run to command, start to run.the only thing i can think of that i did'nt check, was the amps and compare with name plate because compressor could be lock rotor depending on amp reading. and i did'nt check the compacitor under load, any information would be helpful.
jacob perkins
07-12-2005, 06:19 PM
Try the Supco combination relay start capacitor?
j carter
07-12-2005, 06:41 PM
my thoughts as well i will try a hard to start kit, and check everything once again.
condenseddave
07-12-2005, 08:32 PM
I thought the command terminal and the start terminal were the same thing...
jacob perkins
07-12-2005, 10:01 PM
I think he misspelt "common".That's ok.What I noticed was the start to run reading.It might also be a typo?
jc,you could also try to reverse the motor for a second..that will sometimes unlock the compressor.
Didn't do well spelling capacitor either.
j carter
07-13-2005, 07:55 AM
thinks for all the information, please forgive me for mis-spelling words. i will be servicing this unit today the repair will be made, i'll keep you posted.
j carter
07-14-2005, 08:39 AM
serviced unit today and the problem was the compressor it is lock rotor, the hard to start kit could not start it.so i replaced the compressor and everything is good.