View Full Version : Where is the Time Delay-1 Second



hvactech80
04-12-2011, 04:36 PM
We have a Carrier--38AKS--028---500 Condensing Unit--We do not have a Delay on the Part Start Contactors but Looking at the Carrier info--the 50 HZ units do have a Delay--Why would the 60HZ units not have one--Thanks.

S/N--120087875:gah:

flange
04-12-2011, 05:06 PM
isnt it just done via aux contact on starter one? no time delay.

Dallas Duster
04-12-2011, 05:45 PM
If you don't have one then don't worry about it.

duke of earl
04-12-2011, 09:45 PM
No delay means across the line. If the building power drops in voltage when the compressor starts up, get the delay relay. If not, let her eat!