View Full Version : Centrifugal Question



booyah
07-07-2005, 09:37 AM
What is the minimum %RLA that is exceptable for a Centrifugal Chiller - to be specific older Trane CVHE.


Thanks in advance.

greybeard
07-07-2005, 09:54 AM
That would depend on what controls you have on the unit, Generally it will take approx. 15% even with the vanes shut

Carrene #2
07-07-2005, 09:14 PM
Somebody's been reading design spec's.
One thing I do know, you won't be able to run all day at 15%. Discharge temps rise etc., with vanes closed.
Very unlikely that you will get below 30% amp draw with vanes closed.
That 15% is the load the chiller will be able to operate down to, not % amp draw.

greybeard
07-12-2005, 11:24 AM
Actually the 15% is what the control will tolerate before a diagnostic will occur. while I agree that is not a realistic value to expect the machine to run, the question I believe was min. acceptable

Carrene #2
07-12-2005, 07:26 PM
Ok.