View Full Version : high head pressure



cribbetr
07-07-2005, 08:21 AM
HELP!! I evacuated a semi hermetic compressor with R12 as I put the r12 back in the system the head pressure will go 300 to 400psi and trip the pressure switch. what is going on ?

t527ed
07-07-2005, 08:45 AM
discharge valve on compressor closed???? if not that something very very very bad to get those pressures with r-12

onetime
07-07-2005, 09:04 AM
It sure sounds like a valve on the high side is closed or a blockage, bad txv.

LGM
07-07-2005, 03:23 PM
You either had non-condensibles or added them by mistake, most likely. Easy way to check:
- Close liquid line solenoid and let the system pump down.
- Remove a control wire from the compressor contactor.
- Jump out the condenser fan and let run for 1/2 hour.
- Get high side pressure.
- Get ambient temperature.
- Look at P/T chart for the ambient temperature measured. If the pressure is more than a pound or two higher than what it should be (which allows for the gauge to be off a little), you have non-condensibles.

Hope this help.

Makinice
07-07-2005, 06:30 PM
What was the reason for the "evacuation"??
Did you change a system part or something?

R12rules
07-07-2005, 09:09 PM
Back seat your discharge service valve stem and attach your hi side gage to the liquid line at the receiver.


THEN and only THEN ... restart your compressor.

bob1420
07-07-2005, 11:44 PM
overcharged

cphc
07-11-2005, 11:55 AM
overcharge or restriction on high side of system.

dnt
07-11-2005, 08:14 PM
Have you checked water/airflow whichever applies over the condensor coil?

[Edited by dnt on 07-12-2005 at 03:35 PM]