View Full Version : Heat Pump, Not Cooling, w/Strange Readings
phxhvac
07-04-2005, 05:51 PM
I have a package heat pump that is not cooling in the cooling cycle. I have a low amp draw, like 9.3 amps. I think my rating is 23.0 amps, and my gauge pressure is 150# suction, and #150 head while the system is running. It is a TXV system, with no reciever or accumulator. The suction and head seem to be equalized with the system running. The compressor cuts out on internal O/L before it shuts off. Could it be an issue of overcharge? or could it be a compressor with weak valves? I suspect the compressor has weak valves. Has anybody else seen this sort of thing?
__________________________________________________ ________
Thou shall install thermostat covers in public buildings!
[Edited by phxhvac on 07-04-2005 at 11:31 PM]
tlchvac
07-04-2005, 07:08 PM
Your reading the same line my friend:)Where are you taking your readings.....?
robertusa123
07-04-2005, 09:42 PM
if your gage set is hooked up right and it is hot outside to give you 150 readings. itsounds like the compresor is gone
low load amp draw
over heating no freon flow to cool down unit
age?
condition?
Black Adder
07-04-2005, 10:55 PM
Are you taking your readings at the commone suction port? 150 psi sounds like a lot of suction pressure. Also post your line temps, pressure won't tell you what is going on.
phxhvac
07-04-2005, 11:07 PM
I traced the lines back to the reversing valve, the two ports on the outside of the Trane unit. The top one is connected to the middle of the three on the bottom side of the reversing valve(low side)(common suction). The bottom port is connected to the single line on the top of the reversing valve (High Side)(compressor discharge) It is a Trane rooftop package unit heat pump. The Trane unit is either 8 or 9 years old. I wanted to disconnect the condenser fan motor and let the head pressure rise to 475#, then cut out the unit without switching the reversing valve, to see if I have a hot suction line at the compressor or reversing valve line leaking by. But if I had an overcharge, wouldn't the amp draw go higher than the nameplate rating??? This unit is located in a clubhouse of an apartment building.
__________________________________________________ ________
Thou shall install thermostat covers in public buildings!
[Edited by phxhvac on 07-04-2005 at 11:32 PM]
docholiday
07-04-2005, 11:14 PM
Sounds like a bum compressor, valves or broken shaft.
t527ed
07-04-2005, 11:50 PM
sounds like broken compressor
Irascible
07-04-2005, 11:55 PM
Your statements imply that it may be heating OK. Are the pressure readings normal in the heat cycle? If so then you probably have a reversing valve that's sticking.
phxhvac
07-05-2005, 12:00 AM
Didn't try heating cycle it is over 110 degrees here in Phoenix!
Irascible
07-05-2005, 12:16 AM
Pfft. And your point? ;)
You could try it for a few seconds just to see if the reversing valve is willing to move. Though if the readings are truly identical on both sides then it is probably a blown compressor. Even a stuck reversing valve isn't likely to completely equalize things.
dexman
07-05-2005, 01:14 AM
Never seen suction pressure that high. My gauge only goes to 120 psi. I have had psi at 110 due to extreme indoor temp and unit cooling fine but no equal pressures. Sounds like that compressor is what I call "freewheeling". (broken crank?)
j-man04
07-05-2005, 07:31 AM
with both pressures being the same id say its dead compressor where do i get suction gauge that reads 150psi
robertusa123
07-05-2005, 07:50 PM
if itas a roof top unit in 110 heat the sitting psi will be 150 easy
anyone ever herd if a psi temp chart freon only needs to be about 85 to give a psi of 150
schmuck
07-05-2005, 08:29 PM
Where did you amp it at?
dexman
07-05-2005, 10:28 PM
Good point Rob. Didn't consider the chart. Hardly see readings like that in NC
phxhvac
07-05-2005, 11:24 PM
I used my high side gauge on the suction and read 150# Just for the heck of it. My suction was pegged at 120# on the gauge. Amped it at contactor load side.
[Edited by phxhvac on 07-05-2005 at 11:29 PM]