06-23-2005, 06:29 PM
Arrived at job. Lady said, there was a water leak in the bsmt. This renovation comp. came, dug-out and installed new wheeping tiles. While doing that, they disconected the A/C and moved it. Re-connected it after they finished.

A/C, of course, was not working immediately thereafter.

So, I put my gauges, and what do I see. S.L. 25psig, L.L. 500 psig (it took only 3-4 seconds to reach 500 psig). Luckily I was fast enough to pull the plug on the 240 V disconnect box. This is Concord 2 ton installed in 2000.

Oh, I forgot, this renov. comp. actually burried both coper pipes underground.

Compressor was drawing 9 AMPS (plate says 10.2 AMPS).

Apparently there is a restriction - the question is where is that ?

BaldLoonie
06-23-2005, 06:35 PM
Full of air probably. A restriction would just condense the refrigerant in the outdoor coil and your head wouldn't skyrocket.

bananaboy
06-23-2005, 06:41 PM
BaldLoonie "...Full of air probably...."


Well, that's what I though first, but then I decided if the system is full of air - would not the S.L. reading be HIGH too ?

It is only 25 psig on the S.L.

AIR PRO
06-24-2005, 03:36 AM
I'll take both lines kinked/crushed under the slab for $200 Alex.

ct2
06-24-2005, 12:00 PM
and i will take

" How does air get into a sealed system " for $100

Mr Bill
06-24-2005, 12:07 PM
Originally posted by bananaboy
While doing that, they disconected the A/C and moved it. Re-connected it after they finished.

There is you answer a big old restriction, they should have called an a/c company to take a/c loose and reinstall, when did renovation company's start taking on the liability of removing a/c units? :rolleyes: