hello everyone, I'm working on a new install we installed (2)4ton and (1) 5ton A/C units with new furnaces and duct work. All the units are doing the same thing so I just posted the 5 ton.... On day 1 I thought I had an air flow problem so I got a dwyer manometer to measure external static pressure. I got neg.08 in the return and pos.1 in the supply (using a probe) add the two together and get .18 Furnace spec. cfm on chart .2 on hi speed is 2175cfm so that looked OK. I have never used one of these before so did I do that correctly?
I decided to remove some gas because the superheat was so low but this does not seem right because I measured the line set and added 5oz planning to add 1oz more. On day 2(today) the book called for 12f superheat so I pulled out 10oz to get 12f. Should my evap temp be that low? what am I missing? I never get to work on an AC unit with the building this cold so I'm not sure what to think. Thanks.
carrier cond. 38ezg060500
evap ck5bxa060024aaaa
carrier furnace 58mxa 100-20
10 feet extra line set added 5oz 410a
day1
outside air 82db 65wb cond.TD 20f
evap air 76db 65wb TD 21f
SL temp@cond. 38f
LL temp@cond. 92f at evap 89f
low side 112psi/38f superheat 0f
high side 320psi 98f
day2
removed 10oz 410a
outside air 77db
evap air 76db 61wb TD 10f
SL temp@cond. 45f
LL temp@cond. 88f at evap 85f
low side 100psi/33f superheat 12f (book called for 12)
high side 300psi/96f
I decided to remove some gas because the superheat was so low but this does not seem right because I measured the line set and added 5oz planning to add 1oz more. On day 2(today) the book called for 12f superheat so I pulled out 10oz to get 12f. Should my evap temp be that low? what am I missing? I never get to work on an AC unit with the building this cold so I'm not sure what to think. Thanks.
carrier cond. 38ezg060500
evap ck5bxa060024aaaa
carrier furnace 58mxa 100-20
10 feet extra line set added 5oz 410a
day1
outside air 82db 65wb cond.TD 20f
evap air 76db 65wb TD 21f
SL temp@cond. 38f
LL temp@cond. 92f at evap 89f
low side 112psi/38f superheat 0f
high side 320psi 98f
day2
removed 10oz 410a
outside air 77db
evap air 76db 61wb TD 10f
SL temp@cond. 45f
LL temp@cond. 88f at evap 85f
low side 100psi/33f superheat 12f (book called for 12)