View Full Version : Charging a York Centrifugal R123 Chiller



baise
06-20-2005, 04:31 AM
What is the recommended method to add additional charge? Should the charge be sucked in or pumped in? The manual does not specify.

maustin
06-20-2005, 05:49 PM
Place the unit in a vacuum and pull it in.

cold-n-mode
06-20-2005, 06:28 PM
If you do not know how to put the refrigerant in you should not try it .I say this hoping you do not suck the machine full of air trying to add some charge to it.The charging valve is located below the condenser it has a ball valve on it usually with a 5/8 male flare adapter on it.If the chiller is running or setting in a vacuum you can let the machine draw it in.

Carrene #2
06-20-2005, 10:12 PM
http://www.isc.tv/pdf/msdsr123.pdf
Check out the MSDS. You might want to be careful on how much you inhale( like all refrigerants ).

chiller mekanik
06-20-2005, 11:22 PM
Why do you think you need more refrigerant?

RichardL
06-21-2005, 07:15 AM
Yiiiiiiikes!!!!!!!
This is getting "Scary"!!!!!

maustin
06-21-2005, 09:55 AM
A simple question deserves a simple answer. Lets not read more into someones post than what is really there.

baise
06-22-2005, 02:43 AM
maustin ........... very well said!

baise
06-23-2005, 04:52 AM
thanks for the help!