On a contactor it gives two contact amp ratings. FLA is obivious. Does the resistive rating deal with loads other than motors?
cxagent
05-20-2005, 11:23 AM
Yes, non-iductive loads. But in HVAC that only "resistive loads" I can think of are electric heat strips.