Well it's not new but I posted it in the wrong forum. I'm having a problem where I keep getting a communication failure on SBC2 stats. It happens almost once a week where all stats come up with a red flag and show 0.0 degree reading on my front end computer. Have to cycle control power to the controllers to get stats to reset. I was wondering if anyone else had this problem and know's what might be causing it, other than a power failure. VAV controllers are SBC-VAV1, and room sensors are STAT 2, the two button type with no digital display.
davem
04-25-2005, 12:58 PM
It might be related to the Tech Tip Auto-Matrix posted last June. While it deals specifically with the STAT3, it might point you in the right direction:
Subject: SBC-STAT3 displays the wrong value or no value at all when connected to an SBC- or NB-Series Controller.
Description: When an SBC-STAT3 does not draw enough power, the SBC- or NB-Series controller may recognize it as an analog device, leading to incorrect temperature readings, the STAT resetting, or the display going completely blank.
Solution: Depending on the specific problem observed, the solutions are as follows:
Problem: STAT displays the correct temperature, but resets approximately every minute.
Solution: Install a 10k resistor in parallel with the STAT3.
Problem: STAT displays 137 or 138 and then resets.
Solution: Install a 3.3k resistor in parallel with the STAT3.
Problem: STAT display is blank, but a value of 137 or 138 can be read using SoloPro/Nb-Pro.
Solution: Install a 1.5k resistor in parallel with the STAT3.
Additional Tip: This problem is currently being addressed by Engineering and a firmware solution should be available in approximately 2 weeks.
Not sure if your STAT's are digital or analog, but this might help you...
jim reynolds
04-25-2005, 01:20 PM
Thanks it's something to go on.