02-05-2011, 08:56 AM
Md# GY9S120D20UP11J, furnaces are twinned together (5 ton evap. on each furnace) & sit on return box. Total cfm (checked with flow hood) with merv 7 filters, fan on high speed is 2458. Manual states 3400 cfm when twinned. Removed filters, cfm 3244.
Removed blower doors, cfm 3310
Heres my question: return box has two 16x25x1 filters (one under each furnace). The filter rack is built into the return box the furnaces sit on. The install manual states this md. furnace requires a 22x25x1 filter, I obviously have a lot of area blocked off due to smaller filter rack under each furnace. Is this most likely my problem with low airflow?
Sorry, no pics
Thanks for any input!
Removed blower doors, cfm 3310
Heres my question: return box has two 16x25x1 filters (one under each furnace). The filter rack is built into the return box the furnaces sit on. The install manual states this md. furnace requires a 22x25x1 filter, I obviously have a lot of area blocked off due to smaller filter rack under each furnace. Is this most likely my problem with low airflow?