fixerup
04-20-2005, 10:11 PM
I worked on a carrier 17DR today that has a trane purifier purge.I myself have installed quite a few trane purges on carrier chillers.I typically use the service valve on the top of the condenser for my pick up line and use the old purge pick up line(after drilling it out and retapping for a 1/2" angle valve) for my liquid return.The one I worked on today was installed with the liquid return going to the bottom of crossover before the evaporator.Does anyone know if this is ok.Seems to me that the purge would not have enough flow through it to remove noncondensibles.Will the flow become stagnant.Chiller did have some noncondesibles present today.Valved off purge and suction line temp. pulled down to -5.1F opened valves to put purge in operation and suction line temp. rose to 90F.