View Full Version : POE OIL FOAMING
ammoniaman33
01-22-2011, 09:57 AM
RECENTLY REPLACED 20 TON DISCUSS COMPRESSOR ON R-22 FREEZER. FLUSHED ENTIRE SYSTEM WITH NITROGEN AND REPLACED TXV BONNET.
PULLED VACUUM FOR 8 HRS TO 500 MICRONS.
REPLACED FREON , ADDED ACID NEUTRALIZER TO OIL. REPLACED DISCHARGE OIL SEPERATOR, LIQUID INJECTION DRIER AND BURNOUT CORES IN LIQUID LINE.
CHARGED SYSTEM WITH 120 LBS R-22 AND AM GETTING A LOT OF FOAM IN CRANKCASE SIGHT GLASS. DON'T KNOW IF LIQUID INJECTION CONTROL IS BAD
OR WHAT? COLD COMPRESSOR WAS RUNNING WHEN I SHUT IT DOWN, HAD BAD VALVES AND WOULD NOT PUMP DOWN.FREON SMELLED BADDD.
I AM MAINLY AN AMMONIA TECH, BUT DO SOME FREON.
indy2000
01-22-2011, 10:06 AM
hot pull down?
compressor amperage?
are you positive POE is being used? expensive oil for HCFC refrigerant.
k-fridge
01-22-2011, 10:09 AM
Welcome to HVAC-Talk.
This is mainly the new member welcome forum. You'll get more help in the proper forum, in this case the Refrigeration and Ice making forum.
jpsmith1cm
01-22-2011, 10:14 AM
I'm with k-fridge.
Repost this in refrigeration and ice-making along with some more system details like pressures and temperatures and we can discuss this in more detail.
Tech23
01-22-2011, 06:46 PM
Welcome to the site ammoniaman33,
I can't help with your issue, but wanted to say hello.
Good luck and take care.
ammoniaman33
01-25-2011, 02:14 PM
THANKS FOR REPLY GUYS, I DID TALK TO A KRAMER ENGINEER AND HE SAID I WAS DOING EVERY THING RIGHT SO FAR, BUT WASEN'T SURE ABOUT THE OIL FOAMING. COMPRESSOR SUPERHEAT IS A LITTLE HIGH BUT NO FLOOD BACK,
OIL FOAMS UP ON PUMPDOWN AND COMES BACK AFTER DEFROST ENDS.
THINK MAYBE LIQUID INJECTION MODULE IS BAD OR ACID KILLER IS CAUSING FOAM ? SUCTION PR 12PSIG, DIS PR 200PSIG,EVAP SUPHT ABOUT 10*.
seuadr
01-25-2011, 02:38 PM
YOU COULD CONSIDER TURNING YOUR CAPS LOCK OFF, JUST A THOUGHT!
ammoniaman33
01-25-2011, 04:10 PM
seuadr; YOU COULD CONSIDER A MORE PROFESSIONAL MEMBER RESPONSE, JUST A THOUGHT.
chuckcrj
01-25-2011, 04:17 PM
seuadr; YOU COULD CONSIDER A MORE PROFESSIONAL MEMBER RESPONSE, JUST A THOUGHT.
Caps lock on makes it look like you're shouting.
As k fridge said please post this question in the Refrigeration and Ice Making Forum. Here is a link;http://hvac-talk.com/vbb/forumdisplay.php?s=&daysprune=&f=12
You will maybe get some more answers.
ammoniaman33
01-25-2011, 04:39 PM
:oops:sorry bout that, thanks for the info.
jpsmith1cm
01-25-2011, 04:56 PM
Are you having any problems or did you just notice the foaming oil?
Foaming isn't abnormal during pumpdown.
ammoniaman33
01-25-2011, 05:21 PM
thanks for the reply, this is a replacement comp and oil is foaming while running but pump down causes oil to foam up and leave comp ?
just started on this website trying to find my way around.
jpsmith1cm
01-25-2011, 05:32 PM
How high is the oil level?
Could the crankshaft be hitting the oil during operation?
ammoniaman33
01-25-2011, 05:53 PM
i don't see oil splashing on sight glass, just light foam on top and oil gets darker toward the bottom of glass. this an old kramer dual comp package on a 0* freezer, each system has 20 tn evap. hey thanks for the chat, im going off line but if you come up with any ideas it would be greaty appreachted
indy2000
01-25-2011, 07:04 PM
sounds normal.
Why use poe with hcfc?
tjc76
01-25-2011, 07:09 PM
Ammoniaman- welcome to the site.
Is this Kramer unit electric defrost, or is it hot gas?
If it is hot gas, make certain that the thermobank is full of water and that the holdback valve is functioning. Also, you said dual compressor. If this is a dual compressor unit, it probably is also dual bank, and they are a real pain in the arse to set up for floodback control in defrost.
As stated by others, reposting in Refrigeration and Icemaking will get your thread more views, and probably more responses.
This doesn't belong here. Start another post in the proper site area.