PDA

View Full Version : latching and non latching diagnostics



key
04-02-2005, 09:48 AM
This is a microprocessor question I recenlty wrote. Can someone please explaine the difference between latching and nonlatching diagnostics.

kcl
04-02-2005, 10:07 AM
A latching diagnostic results in unit shutdown after an alarm and requires the unit to be manually reset in order to perform a restart. Latching diagnostics are usually more serious alarms such as high head pressure, low refrigerant temperature, starter faults. Non-latching alarms will result in unit shutdown and after the microproceesor senses the alarm condition is corrected the unit will automatically restart without pressing a reset button. Non-latching diagnostics may be from loss of chilled water or condensor water flow. Manufactures will list which alarms are latching or non-latching in the operation manual.

flange
04-03-2005, 08:01 PM
Most times a latching relay will require power to be turned off then back on to reset.

key
04-04-2005, 08:52 AM
Thanx guys

caosesvida
04-04-2005, 10:14 AM
on ddc systems the latching relays can be reset ( the ones that I work with anyway) from your terminal. On the stand alone units they may need to turn off and then on again, if there is not a reset (such as on hps).