View Full Version : screw compressor
orland25
03-28-2005, 06:27 PM
Hi friends; OK I am a little confused with a noise. I 100 TON screw comp, with economizer too,this chiller is york model YCAS0440E. Four compressor in the unit.Ok I listen a noise inside the compressor like a AIR LEAK. All pressure it/s OK but I listen that noise. Any idea to be appreciated
joeywpittman
03-28-2005, 06:49 PM
try to explain the sound that you heard in more detail.
orland25
03-28-2005, 07:10 PM
it/s like you press the (spray can)noise shshshshshshsh
orland25
03-28-2005, 09:21 PM
any idea about that noise?
freeon king
04-06-2005, 06:37 PM
does it have hot gas bypass?
richvito
04-06-2005, 09:07 PM
Liquid injection......................................... ..
tech cr
04-06-2005, 09:29 PM
It could be the internal relief valve in the compressor. I wouldn't worry too much about it. Unless it causes problems.
service guy
04-06-2005, 09:31 PM
Originally posted by tech cr
It could be the internal relief valve in the compressor. I wouldn't worry too much about it. Unless it causes problems. WHAT?????
tech cr
04-06-2005, 09:33 PM
opps! Its a screw compressor. Some recips have internal reliefs.
[Edited by tech cr on 04-06-2005 at 10:13 PM]
jtricor
04-06-2005, 10:12 PM
Not related to the ssssssssssssssssssssssshhhhhhhhhhh noise
but what does an economizer do on a chiller?? or is it really a low ambient control
joeywpittman
04-06-2005, 10:22 PM
no, it is an economizer.
it economizes
djken
04-07-2005, 08:55 AM
Economizer = Motor cooling
joeywpittman
04-07-2005, 09:33 AM
the Economizer is a refrigerant to refrigerant, compact
plate-type heat exchanger to maximize chiller capacity
and efficiency by subcooling liquid refrigerant
delivered to the cooler expansion valve.