I got a 23XL Carrier screw chiller that just had it’s Benshaw soft starter replaced (complete RSM6B unit). The chiller was down approximately 5 weeks. Upon attempting startup, the chiller faults on “High Condenser Pressure”. The condenser pressure read about 80 psi, which coincides with the oil pressure reading. The discharge transducer is good. The threshold value is set at 230 psi. The discharge pressure switch and the CW and CDW differential pressure switches were closed. There were no faults displayed on the starter. Benshaw shall be contacted on Monday. Does anyone know what the problem may be? Thanks.
Air cooled or water cooled? Fans running? Water flow? Water valves open?
Water cooled. CW and CDW differential pressure switches were closed.
joeywpittman
03-27-2005, 05:26 PM
HCFC-22 or HFC-134a
joeywpittman
03-27-2005, 05:33 PM
[HIGH CONDENSER PRESSURE] Condenser Refrigerant Pressure VALUE exceeded limit of [LIMIT]*.
Check condenser water and transducer.
Check for high condenser water temperature.
Check transducer accuracy.
how do i know, that you know, the transducer is accurate. what did u do to check it?
[Edited by joeywpittman on 03-27-2005 at 05:37 PM]
joeywpittman
03-27-2005, 05:43 PM
Capacity Overrides (Table 5) — These can prevent
some safety shutdowns caused by exceeding motor amperage
limit, refrigerant low temperature safety limit, motor high
temperature safety limit, and condenser high pressure limit.
In all cases there are 2 stages of compressor slide valve
control.
1. The slide valve is held from closing further, and the status
line on the LID indicates the reason for the override.
2. The slide valve is opened until condition decreases below
the first step set point, and then the valve is released
to normal capacity control.
Whenever the motor current demand limit set point is reached,
it activates a capacity override, again with a two-step process.
Exceeding 110% of the rated load amps for more than
10 seconds will initiate a safety shutdown.
Using R-22
Condenser water pump running and valves open. Condenser water proof of flow differential pressure switch closed. Discharge transducer was replaced (although 80 psi should not have signaled an alarm in the first place). Also did a system transducer auto check.
I should make it clear that the unit has never actually started since the soft starter replacement. The unit alarms when attempting to start up. The current condenser pressure flashes on the LID and the message “High Condenser Pressure” is displayed.
I suspect that maybe the alarm message may not accurately define the true problem. Reason: I use to get a nuisance alarm that stated “Starter Auxiliary Run Contactor Fault”, which is actually not applicable to an electronic soft starter. But the alarm message did tell me that there was some type of problem or glitch with the soft starter.
Thank you for your responses.
joeywpittman
03-27-2005, 07:13 PM
activate the Capacity Override for high condensing pressure
joeywpittman
I'll look into the Capacity Override first thing tomorrow. Thanks
techtalker
03-28-2005, 01:28 PM
Here's the deal:
When the controls try to start the chiller, they close the 1CR control relay which is in the starter and tells the benshaw unit to start. The controls then look for a start initiated reply back from the starter within 2 sec., which is the 1M contact closure. If the controls do not see this 1M contact closure, then they give the high condenser pressure alarm, because there is also a condenser high pressure switch in the 1CR circuit.
bottom line: Look for a reason why the benshaw starter is not starting
techtalker
Although my SCR soft starter does not utilize 1CR and 1M relay/contractor, I believe that you may be right that the problem is at the starter. Will be looking further. Thank you.
joeywpittman
03-29-2005, 09:44 AM
pbcd
check out this link
http://www.xpedio.carrier.com/idc/groups/public/documents/bulletin/c0113-rcd.pdf
bradysmill
03-29-2005, 10:17 PM
Originally posted by techtalker
Here's the deal:
When the controls try to start the chiller, they close the 1CR control relay which is in the starter and tells the benshaw unit to start. The controls then look for a start initiated reply back from the starter within 2 sec., which is the 1M contact closure. If the controls do not see this 1M contact closure, then they give the high condenser pressure alarm, because there is also a condenser high pressure switch in the 1CR circuit.
bottom line: Look for a reason why the benshaw starter is not starting
pbcb,
Here is your answer-----I had the same thing happen to me too.....turned out to be what techtalker said here.
Still troubleshooting with Benshaw. Will talk to Benshaw tomorrow about the jumpers on the computer card not matching the schematic nor the existing card.
Problem resolved. Removed jumper on the I/O board for ISM start and solder in new jumper for Standard start. techtalker: you were right, it was the starter.
Thanks everyone for your help!