View Full Version : York package rtu 5 ton // heating problem
danmatney
01-09-2011, 08:36 PM
I cant get the york rtu to fire in heat mode . i replaced the board , the spark ignition board , can not find any safety switches open , i have 24 volts out of the board but nothing at the igition board. inducer fan runs , but im lost now. any help?
its a small 5 ton unit M#D7CG036N07925A
BKS60
01-09-2011, 09:03 PM
Start at the board and follow till 24v stops. Lay odds on draft motor switch or roll out.
jtrammel
01-09-2011, 09:17 PM
its got to be open somewhere. look at schematic and find all limits then check them. they can hide them in hard to find places sometimes. blower compartment ect.
Trane Guy LI
01-09-2011, 10:14 PM
Somthing has to prove draft. Pressure switch?
danmatney
01-10-2011, 09:37 PM
ok it was an aux safety located in the heat exchanger section on the wall by the compressor section had to take the top of the unit off and the condenser fan out and there is no pressure switches on that york roof top unit it has a centrifugal switch on the bottom of the inducer motor. I love engineers that never had to service something . they should all have to do at least a year in the field on a roof when its 10 degrees and covered with snow and ice. OK GUYS it looks and works good on paper . gees
jackintheboxtec
01-10-2011, 09:48 PM
There is usually an access panel on the opposite side of the unit from the burner section. So you can access the heat exchanger.
BKS60
01-10-2011, 09:48 PM
Well crap I lost.
Of course I didn't say how much I was betting!
Just for some future info I have seen the rollouts that would hold for a couple of seconds then open. It makes for a hard diagnosis. Glad you solved your problem.
supertek65
01-10-2011, 10:06 PM
did you check the high limit in the HX section?
supertek65
01-10-2011, 10:07 PM
nevermind!!!!!!!!!!!!!!!!!!!
PortaChill
01-11-2011, 01:41 AM
Hey there Dan, If it was the aux. High Limit that opened then you may want to check out your air side of the system(blower,ducting ect.). That safety is there so the unit does not catch fire...
Texas-Tech
01-11-2011, 07:56 PM
Funny, I had one of those units today with the same problem. Just reinforced my belief that that model is a PIA
supertek65
01-11-2011, 07:59 PM
http://www.gameguru.in/images/gta-iv-ps3-bundle-confirmed.jpg
Funny, I had one of those units today with the same problem. Just reinforced my belief that that model is a PIA
flange
01-11-2011, 08:17 PM
036 isnt five ton
supertek65
01-11-2011, 08:19 PM
it is not 7200 btu's per ton?
dam!
when did they change that?
036 isnt five ton
timebuilder
01-12-2011, 03:40 PM
Looks like it would be a good idea to check out the thread in this section on wiring diagrams. I will post links to the articles tonight.