PDA

View Full Version : Possible bad cap situation on my outside fan unit? (35mfd was replaced with a 7.5)



ap42
01-09-2011, 12:54 PM
Our downstairs AC went out last August and our home warranty folks sent out a serviceman to fix it (dual zone heat pump setup). He said it was a bad capacitor & replaced it. Our AC worked again and we were happy.

Now it's winter and I noticed the downstairs wasn't warming very well & the thermostat says "heat 2 pump". The fan unit outside is not running at all, and I don't notice any sounds coming from it when I flip the circuit breaker (the upstairs fan unit is running like I'd expect). I guess the "heat 2 pump" means that the air handler is heating the air with the electric heater strips instead of using the heat pump with the fan unit.

So I opened up the service panel on the fan unit to see if anything looked burnt. I noticed that the repairman zip-tied the new (much smaller) capacitor to the old one and rerouted a couple connections to it, but left the old one mostly hooked up. Either that, or he replaced an old 3-terminal one with 2 dual-terminal ones in such a way as to work the same as the old one? I only suggest that since both capacitors look pretty shiny & new with no bulging. I didn't try to disconnect them to test them with a meter since I don't really know what I'm doing.

The big cap in the back is 35mfd. The little one is 7.5mfd. I forgot to take a pic of how they are hooked together - I can get that if it would help.

I'm going to attach a couple pics in the hope that someone could mention if it looks fishy. I plan on making a service call tomorrow but want to know if I should complain about the current capacitor situation. Or is this a normal way to use two dual-pole caps to replace a dead 3-pole cap?

The last pic is of the unit's label: unit # & serial number if it helps. It's a Carrier brand.

Thanks!

SonicExplorer
01-09-2011, 01:05 PM
I'm not an HVAC expert, and keep in mind the pics make it a bit difficult to see the connections, but if I'm seeing things correctly then it looks like you had a single tri-pole replaced by two bi-pole start capacitors. If that is the case then you should be fine, at least WRT to the configuration. Whether or not the caps are functioning or properly sized is another story.

mgenius33
01-09-2011, 01:09 PM
The old dual capacitor he removed, and put two in it's place. It's fine, actually probably better for heat dissipation. Even better he used 440v caps instead of 370v. Not needed for the fan though, can't quite see the 35µf, but probably a 440v as well. 35µf sounds right for a 2ton.
I probably wouldn't have zip tied them together, but it's not hurting anything. I just prefer strapping them separately if there is room.

Capacitors fail for a lot of reasons. It could be power surge, power dip, thunderstorms, failing compressor, bad capacitor itself (they're made cheap now-a-days), excessive heat...etc

ap42
01-09-2011, 01:55 PM
Thanks for the replies - they give me some peace of mind. I'm going to call the same folks to have them take a look at what is wrong with it now. Maybe one of the caps went bad again, or maybe the motor or compressor is dead. The fan spins freely when I spin it, but I have no idea how to diagnose what is wrong. Plus it's going to be pretty cold in the foreseeable future with some snow, so I'd like to get the heating back up to par as quickly as possible. Too bad my home warranty has expired.

I did turn the thermostat to 'cool' and set it to 65 and verified that the fan & compressor did not come on after a few minutes.

- Anthony

SBKold
01-09-2011, 02:07 PM
Try resetting the breaker labeled Heat or Air Handler.

bwalley
01-09-2011, 02:15 PM
Thanks for the replies - they give me some peace of mind. I'm going to call the same folks to have them take a look at what is wrong with it now. Maybe one of the caps went bad again, or maybe the motor or compressor is dead. The fan spins freely when I spin it, but I have no idea how to diagnose what is wrong. Plus it's going to be pretty cold in the foreseeable future with some snow, so I'd like to get the heating back up to par as quickly as possible. Too bad my home warranty has expired.

I did turn the thermostat to 'cool' and set it to 65 and verified that the fan & compressor did not come on after a few minutes.

- Anthony

it probably had a 35/7.5 dual capacitor and he replaced it with 2 individual capacitors, could have done a little nicer job on the install but it works.

Probably lost a capacitor, not a big deal, its frustrating but it happens, it seems like we have either been getting bad capacitors lately or spikes are taking them out, sucks for the customer to have to pay for another repair.

I only buy cpacitors rated at 440v,the capacitor he used is made in china so the quality control is pretty much non existant, unfortunately more and more stuff is being made in china, I don't think my supplier has any capacitors that aren't made in china.

basshound71
01-09-2011, 02:17 PM
Pretty common practice to do it that way as most parts houses don't carry dual caps.

ap42
01-09-2011, 02:34 PM
I turned off the circuit breakers for the downstairs AC & heating unit (which I'm pretty sure is for the compressor/fan outside & the air handler under the house). Counted to 10, turned them back on, and everything is the same. The air vents are blowing slightly warm air, the thermostat flashes "heat 2 pump", and the unit outside isn't doing anything.


I have a question on testing the caps: if I turn off the breaker, do I have to disconnect the caps before I can discharge them with a screwdriver to test them? I would think so to avoid hurting anything it is connected to?

I only ask because it turns out one of my multimeters has a capacitance setting, and I thought I could try hooking it up to see if they are within spec.

bwalley
01-09-2011, 02:36 PM
I turned off the circuit breakers for the downstairs AC & heating unit (which I'm pretty sure is for the compressor/fan outside & the air handler under the house). Counted to 10, turned them back on, and everything is the same. The air vents are blowing slightly warm air, the thermostat flashes "heat 2 pump", and the unit outside isn't doing anything.


I have a question on testing the caps: if I turn off the breaker, do I have to disconnect the caps before I can discharge them with a screwdriver to test them? I would think so to avoid hurting anything it is connected to?

I only ask because it turns out one of my multimeters has a capacitance setting, and I thought I could try hooking it up to see if they are within spec.



This isn't a DIY site and we aren't supposed to tell you how to do it yourself and i probably already said too much inmy previous post.

ap42
01-09-2011, 02:42 PM
This isn't a DIY site and we aren't supposed to tell you how to do it yourself and i probably already said too much inmy previous post.

Understood. Thanks for the response - hopefully it will be a cap & be an easy same-day fix for the repairman.

bwalley
01-09-2011, 02:47 PM
Understood. Thanks for the response - hopefully it will be a cap & be an easy same-day fix for the repairman.

it looks like the repair was done about 6 months ago, if it was my company that did the repair, I would warranty it, but since a home warranty company paid for the repair and the a/c contractor probably got paid peanuts for the repair, you will proably have to pay for it.

since the compressor and the fan aren't coming on, it may not be the capacitor's, it is probably something else very minor.

JJDH
01-09-2011, 06:14 PM
it looks like the repair was done about 6 months ago, if it was my company that did the repair, I would warranty it, but since a home warranty company paid for the repair and the a/c contractor probably got paid peanuts for the repair, you will proably have to pay for it.

since the compressor and the fan aren't coming on, it may not be the capacitor's, it is probably something else very minor.
Ooh ooh me,me, i know, pick me, me,:munching:

ap42
01-10-2011, 12:14 PM
It turns out there was a coolant leak at the outside unit. There's a thin coolant line going from the compressor that had some power wires rubbing against it. One of the wires wore through to the copper, and it looks like there was some arcing that burned a hole int he copper line. When pressure is applied to the system it leaks like crazy.

The tech will be back later (he ran out of juice for his torch) to try to solder it up. With any luck that will fix us up while we decide whether to replace the outside system or if we want to replace the entire HVAC to a more efficient one.

He said to brace ourselves for a big electric bill this month. :)

ap42
01-10-2011, 12:35 PM
Took a few pics. Apparently the wires used to be ziptied out of the way, but the ziptie broke & they started rubbing away with the fan vibration. I was suprised how big the hole was.

Roadhouse
01-10-2011, 12:41 PM
It turns out there was a coolant leak at the outside unit. There's a thin coolant line going from the compressor that had some power wires rubbing against it. One of the wires wore through to the copper, and it looks like there was some arcing that burned a hole int he copper line. When pressure is applied to the system it leaks like crazy.

The tech will be back later (he ran out of juice for his torch) to try to solder it up. With any luck that will fix us up while we decide whether to replace the outside system or if we want to replace the entire HVAC to a more efficient one.

He said to brace ourselves for a big electric bill this month. :)

Correction my friend, refrigeration systems have no coolant in them to leak, they have refrigerants.

Funny but someone else on an entirely different thread was wondering aloud about why not to just wrap a resistive for defrost wire throughout a coil with refrigerant running through that coil. It was then brought up that if the wire arced or shorted or even got too hot it could burn a hole right through the copper and leak not coolant but rather refrigerant and here we are with the proof.

Thanks.

Roadhouse
01-10-2011, 12:49 PM
Took a few pics. Apparently the wires used to be ziptied out of the way, but the ziptie broke & they started rubbing away with the fan vibration. I was suprised how big the hole was.

Those are 120 volt wires which btw with a load on any electrical circuit (when the compressor is on and running it's pulling a load, when it is off and not running there is no load) the bite is much worse than it's bark, comparatively.

Yes, those zip ties are out doors and so in the elements and are more prone to fail, as with anything in the constant elements, vs. indoors. They probably got hot themselves and along with being dry rotted from the heat of the compressor and sun, they just broke.

Gald it was simple fix for you.

keeplearnin
01-10-2011, 01:15 PM
yes in either case it's not a free ride get your checkbook out.

bwalley
01-10-2011, 03:38 PM
It turns out there was a coolant leak at the outside unit. There's a thin coolant line going from the compressor that had some power wires rubbing against it. One of the wires wore through to the copper, and it looks like there was some arcing that burned a hole int he copper line. When pressure is applied to the system it leaks like crazy.

The tech will be back later (he ran out of juice for his torch) to try to solder it up. With any luck that will fix us up while we decide whether to replace the outside system or if we want to replace the entire HVAC to a more efficient one.

He said to brace ourselves for a big electric bill this month. :)

Have him give you a bid to replace the drier, they need to be changed whenever the system is opened up and have him give you a bid on the accumulator, as it is probably rusting and will be your next leak, doing it all at one time will be better than changing it later, then decide if you want to replace the whole system.

If it was my house I would probably just repair the system you got.

The reason you keep 2-3 bottles of gas or more on your truck is so you don't run out of juice.

bwalley
01-10-2011, 03:39 PM
Took a few pics. Apparently the wires used to be ziptied out of the way, but the ziptie broke & they started rubbing away with the fan vibration. I was suprised how big the hole was.

take pictures of the accumulator, it is the big round black thing with two pipes in it and it is probably very rusty.

It isn't the big round black thing with wires hooked up to it, that is your compressor.

ap42
01-10-2011, 05:10 PM
bwalley : I'm attaching a couple pics I had taken of the inside of the fan unit. The second pic is the small black "muffler" thing in the upper-right of the first pic.

The tech (a good guy) fixed the pipe a few hours ago & added refrigerant, then patted me on the back as I cried over the final bill. :)

Things seem to be back to normal for now, and I'm going to have another one of their guys come out to size the house & give an estimate on replacing with a more efficient unit since mine is almost 10 years old. Just so we know what our options are.

Thanks for all the info. I'm glad I found these forums. I need to read up and keep learning.

bwalley
01-10-2011, 05:16 PM
bwalley : I'm attaching a couple pics I had taken of the inside of the fan unit. The second pic is the small black "muffler" thing in the upper-right of the first pic.

The tech (a good guy) fixed the pipe a few hours ago & added refrigerant, then patted me on the back as I cried over the final bill. :)

Things seem to be back to normal for now, and I'm going to have another one of their guys come out to size the house & give an estimate on replacing with a more efficient unit since mine is almost 10 years old. Just so we know what our options are.

Thanks for all the info. I'm glad I found these forums. I need to read up and keep learning.

If it was my condensing unit, I would replace the muffler or remove it and change out the accumulator, remove the drier if it has one and install a bi directional liquid line drier, vacuum it down and recharge the system.

also have the contractor wrap the wires and place them where they won't cause you problems in the future, i have seen this kind of crap happen many times and it is due to bad design and unfortunately the customer (You) have to pay the price.

but you should get a bid on it and weigh that against the cost of a new system.