Dose any of you gents know how to troubleshoot the economizer in this model of lennox rtu.
Let me tell you what I did. I put a jumper of the T and T1 on the A6 module. Than I jumped the fan. And turned the unit on. I turned the potentiometer to 100% and nothing happened. Put on the actuator there is a connection T1 and T and when I put T1 cable to T and the T cable to T1 the acuator moves. So I know that the issue is either the outdoor enthalpy sensor or the A6 logic module. But I dont know how to test either of them
Let me tell you what I did. I put a jumper of the T and T1 on the A6 module. Than I jumped the fan. And turned the unit on. I turned the potentiometer to 100% and nothing happened. Put on the actuator there is a connection T1 and T and when I put T1 cable to T and the T cable to T1 the acuator moves. So I know that the issue is either the outdoor enthalpy sensor or the A6 logic module. But I dont know how to test either of them