View Full Version : Heat Pump Aux Light Blinking
raytoddjr
03-01-2005, 05:05 PM
I have a Rheem heat pump that is 12 years old (the compresser was replaced 1/2004). I have noticed over the past couple of several weeks that the aux light on the thermostat is blinking. If I tap temp up a degree or two, the light comes on steady. If I tap it down a degree it to, the light goes off.
The fact that it is blinking, should I be concerned?
karsthuntr
03-01-2005, 08:55 PM
The defrost board in the OU is bad. Put the t-stat on em-heat and call your serviceman in the morning. If you go outside to the condensor, you will here a clicking that is timed with the light blinking.
If you let it go too long you run the risk of burning up fan relay and reversing valve.
bornriding
03-01-2005, 09:23 PM
Is the thermostat loose on the wall. Any vibrations against the wall??
raytoddjr
03-02-2005, 08:59 AM
The thermostat is not loose in fact I checked that yesterday as well as making sure that it is level...
Thanks for the advice (both of you!)...
Ray.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.