PDA

View Full Version : Fulton Boiler lockout code



indoorcomfrtsl
11-14-2010, 09:41 PM
I am working on a Fulton Vantage Boiler. M/N VTG-3000. The boiler has been locking out requiring a manual restart. The code on the seimens control says -Fan contactor Fan contactor is off. It is giving a code:2A D:00 P:38
Both the air servo and gas servo are in snyc according to the reading on the display while lighting.
Any insight would be appreciated>

FultonBoiler
07-13-2011, 09:07 AM
Hello indoorcomfrtsl, your Siemens control is asking for the fan to energize and it either not pulling in the fan starter/contactor or it is and the pressure switch is not making or there is loose wiring. If the fan is running you should be measuring voltage on X3.02.2 and X3.02.1