A customer asked me to look at a boiler installation they had that was done by another contractor. It is now out of warranty with that contractor. They have had a lot of problems with lockouts.
I checked the installation and found that none of the 4 boilers had been set up properly. Gas pressures were too low, CO2 was outside specs, etc. Got everything tuned up properly and the problems went away we thought. Tune up was done in August before hardly a week went by that they didn't have a lockout before that. Gas pressures were checked and set with all 4 boilers firiing at 100%.
Just this past weekend we had two boilers lockout on gas valve faults and the history log status says boilers were in post purge. All 4 boilers also lost their time of day, date clock data about a week before that too.
Then Friday a third different boiler locked out on gas valve fault. I am suspecting gas pressure problems as I think it unlikely that 3 different 1 yr old boilers would have gas valve problems. However I know that there were some recalls on controls for these boilers. I changed out 2 controllerer in August because they were on the recall list.
Has Weil Mclain solved their control problems with these boilers?
I checked the installation and found that none of the 4 boilers had been set up properly. Gas pressures were too low, CO2 was outside specs, etc. Got everything tuned up properly and the problems went away we thought. Tune up was done in August before hardly a week went by that they didn't have a lockout before that. Gas pressures were checked and set with all 4 boilers firiing at 100%.
Just this past weekend we had two boilers lockout on gas valve faults and the history log status says boilers were in post purge. All 4 boilers also lost their time of day, date clock data about a week before that too.
Then Friday a third different boiler locked out on gas valve fault. I am suspecting gas pressure problems as I think it unlikely that 3 different 1 yr old boilers would have gas valve problems. However I know that there were some recalls on controls for these boilers. I changed out 2 controllerer in August because they were on the recall list.
Has Weil Mclain solved their control problems with these boilers?