10-19-2010, 04:43 PM
Need your help
Been troubleshooting a Hydronic Heating Boiler. Raypak Hi Delta H3 050 2B.
Kept finding unit down in the mornings showing one of two things "Manual High Limit" or "Flow Switch/Pump faillure". Unit would reset and starts as normal then fail again at some point in the day, long story short I found the pump motor tripping on thermal overload, with no flow through the boiler it would hit High Limit in a matter of seconds, if it tripped during overrun period it would come in as Flow Switch faillure. Local distributer wants to sell me a motor/pump assembly for $2,000, I can get motor rebuilt locally but this requires Boiler to be down for two days minimum, I'm looking to simply replace the motor, trhen get this one rebuilt for a spare, any help appreciated. Location is Los Angeles
OEM for pump motor
Emerson
Mdl S55NXLZM-6465
Cat # 1630-065
1/2hp/1725/SF 1.0
115/60/ph1 CODE L
Amps 7.9 sfa Ambient 60c cont. duty
class B insulation
Been troubleshooting a Hydronic Heating Boiler. Raypak Hi Delta H3 050 2B.
Kept finding unit down in the mornings showing one of two things "Manual High Limit" or "Flow Switch/Pump faillure". Unit would reset and starts as normal then fail again at some point in the day, long story short I found the pump motor tripping on thermal overload, with no flow through the boiler it would hit High Limit in a matter of seconds, if it tripped during overrun period it would come in as Flow Switch faillure. Local distributer wants to sell me a motor/pump assembly for $2,000, I can get motor rebuilt locally but this requires Boiler to be down for two days minimum, I'm looking to simply replace the motor, trhen get this one rebuilt for a spare, any help appreciated. Location is Los Angeles
OEM for pump motor
Emerson
Mdl S55NXLZM-6465
Cat # 1630-065
1/2hp/1725/SF 1.0
115/60/ph1 CODE L
Amps 7.9 sfa Ambient 60c cont. duty
class B insulation