PDA

View Full Version : fan switch on a true freezer!



primmers
09-30-2010, 11:41 PM
the one with a red/black/brown wire !! is there a link showing ME how that thing works? testing ect??
theres no cartoon on this reachin..
thanks:gah:

crymtide
09-30-2010, 11:51 PM
Red black and brown means defrost termination/fan delay.

primmers
09-30-2010, 11:54 PM
yes..i know, i have a system that the fans wont come on, evap is frosty and i think they should...i have a new one, but would like to trouble shoot it before i replace it!

t-49f it also has a klikson with 2 small black wires that is attatched to the ceiling of the box..

james122964
10-01-2010, 12:24 AM
yes..i know, i have a system that the fans wont come on, evap is frosty and i think they should...i have a new one, but would like to trouble shoot it before i replace it!

t-49f it also has a klikson with 2 small black wires that is attatched to the ceiling of the box..

the other is defrost safety.

klickson should have the temperature were it operates on it, it also could be wired in wrong.

Jim

did you check the plug in connection for the fans? then come loose and get corroded.

primmers
10-01-2010, 12:36 AM
no one has worked on it but me...and i havent!!

yes the fans are plugged in..

the little klickson is closed!!

icemeister
10-01-2010, 06:37 AM
Here's the wiring diagram for that box.

Check your door switches also. I've seen lots of problems with those.

crymtide
10-01-2010, 08:36 AM
yes..i know, i have a system that the fans wont come on, evap is frosty and i think they should...i have a new one, but would like to trouble shoot it before i replace it!

t-49f it also has a klikson with 2 small black wires that is attatched to the ceiling of the box..

Heat wiil show Def. term the other side depends on temp setting but a walkin freezer should do it

primmers
10-01-2010, 10:48 AM
thanks guys..

primmers
10-01-2010, 06:53 PM
Ok, turns out my fans didnt come on because the grassland timer relay failed..there was a big black spot on the back side of the solid state timer..

timer was noisey when i showed up the 1st time..i should have checked it out 1st....*gulp*

sokoservices
10-06-2010, 12:55 PM
I am a True MFG authorized warranty rep. These defrost timers are the first thing that i check....

JBM1000
10-09-2010, 01:12 AM
On True units with defrost timer, the left upper screw is within 1/32" to the pc board high voltage circuit and if it gets just a hair inward towards the screw head, well, your done. to a direct short making timer useless for much more than a timer.