craig1
09-11-2010, 05:38 PM
I have a market with Hussman Protocol "mini-rack" system that I've been taking care of for the past year. It was installed in '03 and all their old cases were connected to it. At the same time a 10 door ZeroZone reach in was installed. Over the time I've been servicing the store I've watched as the suction stop valve to the ZeroZone became increasingly incased in ice and the suction filter grew into a watermellon sized ball of ice. I suspected a problem, but kept brushing it off as excessive humidity in the basement and no ventilation. The compressors always had plenty of superheat so I didn't really worry about it.
Today I stopped by to pick up some groceries and the owner showed asked me to look at the system. He had opened the door on the protocol and the lead compressor was completely encased in ice and the second compressor partially covered. I found the sight glass flashing and the receiver at 0%.
Since I had previously suspected problems with the zerozone I checked there first. I had to turn both TXVs on the system in 3 turns to get 5 degrees evaporator superheat. after I did this, the ice started melting on the compressor and the receiver level went up to 10% as all the liquid was pulled out of the suction header.
I would normally suspect that the TXV's were never set, or set improperly after installation, but from what I saw happen it seems like the TXV's lost superheat over the course of the year? is that possible? They're Sporlan valves and they are properly installed. I know for sure that no one besides me touched this system over the course of the year.
Today I stopped by to pick up some groceries and the owner showed asked me to look at the system. He had opened the door on the protocol and the lead compressor was completely encased in ice and the second compressor partially covered. I found the sight glass flashing and the receiver at 0%.
Since I had previously suspected problems with the zerozone I checked there first. I had to turn both TXVs on the system in 3 turns to get 5 degrees evaporator superheat. after I did this, the ice started melting on the compressor and the receiver level went up to 10% as all the liquid was pulled out of the suction header.
I would normally suspect that the TXV's were never set, or set improperly after installation, but from what I saw happen it seems like the TXV's lost superheat over the course of the year? is that possible? They're Sporlan valves and they are properly installed. I know for sure that no one besides me touched this system over the course of the year.