View Full Version : Everything works except no water circulation
stevemason5
10-05-2004, 11:03 AM
I have a Sears/Kenmore gas furnace hot water heating system thats acting erratically.
What works:
1.) The house thermostat appears to work.
2.) I hear the electronic igniter "clicking".
3.) I hear the gas supply flowing.
4.) I see and hear the gas ignite and stay lite.
What does not work:
1.) The Grundig circulator pump (which makes a humming sound when it operates) does not appear to be operating (no hum, as before).
2.) The heating system works as described above but seems to cycle on and off without water circulation - the circulator hum is no longer there. In the past, I am 90% sure the circulator pump kicked in whenever the furnace was activated by the room thermostat.
3.) MOST IMPORTANT: When the furnace is activated (by initially raising the temperature setting of the room thermostat) the igniter lites the gas and the furnace runs for a few minutes, then it shuts down. The new room thermostat setting is completely ignored and little heat reaches the room radiators. STATS: The furnace reads a temperature of about 180 degrees F with a water pressure of about 18 psi.
I suspect (but I am likely WRONG) the furnace is reaching a top temperature and then cycling off as a protective measure because the pump is not circulating the heated water to the room radiators and returning cooler water for reheating. What I cannot understand is why the pump does not operate. Also, the furnace temperature reading does not appear to be very "high" (high enough to cause a furnace shutdown) or beyond a normal Winter operating temperature.
Sorry for the long post - just trying to describe the problem.
Thanks for all your help.
Steve
oil lp man
10-05-2004, 12:39 PM
The problem could be the thermostat itself or thermostat connections on the thermostat, or the thermostat connections on the circulator control, or the circulator control itself could be bad, or the 120 volt connections at the circulator control are loose, or the connections at the circulator are loose, or the circulator could be bad or the capacitor at the circulator could be bad.
If you have a volt-ohm meter and know how to use it, you will figure it out.
Its even possible that there is air in the zones and the circulator won't pull.
Chances are the control will only fire off the burners if its calling for heat so that would ELIMINATE the thermostat and connections as being the problem.
[Edited by oil lp man on 10-05-2004 at 12:45 PM]
stevemason5
10-05-2004, 03:52 PM
Thanks oil lp man.
I started checking voltages with an ohmmeter and was about to remove the circulator capacitor when...
I found one loose thermostat connection (left by the furnace man). I tightened it and it looks like its working.
Seems like its almost always 1 or 2 simple things.
I'll post again if anything changes.
Steve
h2045
10-05-2004, 04:27 PM
It`s a boiler NOT a furnace
stevemason5
10-11-2004, 10:29 AM
My hot water circulator problem returned (likely never left).
The room thermostat initially turns on the boiler (igniter clicks, gas flow and flame all present and working) and the circulator operates. It all runs fine for about 15-30 minutes then everything shuts down. The initial shut down ignores the room thermostat. Later, it turns on again. Sometimes, everything including the circulator, works. Other times, the igniter kicks in, the gas flows and the boiler lights and runs, but the circulator does not operate.
Specs around shut off time - Water temp about 185 deg F, water pressure about 13 psi.
I've checked the electrical connections and they look okay but will check again. I do not think its an air pocket. Its circulator operation related.
Help appreciated !
Steve
oil lp man
10-11-2004, 10:41 AM
When it happens again, if you put a jumper across the thermostat connections of the aquastat control and you don't have power(120 volts) at the circulator terminals at the aquastat control(C1 and C2) then your aquastat control is bad.
stevemason5
10-11-2004, 11:52 AM
oil lp man,
I identified the C1 and C2 (circulator) connectors with black and white wires. Also, I found the thermostat connectors as follows:
TV: with a red wire
W jumped to the TV connector
T with a green wire
Z with a white wire
Which two room thermostat wires do I jump (then check C1/C2 for 120 VAC) when the circulator is not working ?
More info:
Inside the Honeywell elctrical housing I found a transformer, a (I believe) gas valve relay and a device with a gear in it with (I think) temperature markings stamped into the metal. I carefully checked and found 120VAC current at the line (L1/L2) connectors. Inside the circulator electrical housing I found connectors and a cylindrical device that looks like a electrolitic capacitor. On the outside of the Grundfos circulator there is a 1" slotted screw in the center of the housing that dripped water a bit when I turned the screw counter-clockwise a half turn (retightened).
Where is the aquastat ?
Steve
oil lp man
10-11-2004, 12:54 PM
Originally posted by stevemason5
oil lp man,
I identified the C1 and C2 (circulator) connectors with black and white wires. Also, I found the thermostat connectors as follows:
TV: with a red wire
W jumped to the TV connector
T with a green wire
Z with a white wire
Which two room thermostat wires do I jump (then check C1/C2 for 120 VAC) when the circulator is not working ?
More info:
Inside the Honeywell elctrical housing I found a transformer, a (I believe) gas valve relay and a device with a gear in it with (I think) temperature markings stamped into the metal. I carefully checked and found 120VAC current at the line (L1/L2) connectors. Inside the circulator electrical housing I found connectors and a cylindrical device that looks like a electrolitic capacitor. On the outside of the Grundfos circulator there is a 1" slotted screw in the center of the housing that dripped water a bit when I turned the screw counter-clockwise a half turn (retightened).
Where is the aquastat ?
Steve
You're scaring me. I thought you had a better idea of what you were doing. The electical housing you are talking about is the aquastat.
You need to jumper the TV and T terminals.
I'm done.
[Edited by oil lp man on 10-11-2004 at 01:00 PM]
hetrola
10-11-2004, 03:33 PM
Your hight limit is shutting the boiler off at 185 deg. Your circ. pump should be running and this is normal. your boiler maintains temperature. if your circ. pump is not running on calls for heat then you should call in a pro.
GradyWhite244
10-11-2004, 09:47 PM
Grundfos circulator? Is the circulator body hot? If it is, the circulator rotor is probably stuck. A common problem with Grundfos.
heatpumpman24
10-11-2004, 09:56 PM
Just a guess, but maybe the control for the pump is bad, or maybe just the pump is bad...
keith1
10-11-2004, 10:44 PM
Gradywhite is right,on the back of the circulator pump is a silver slotted screw.Unscrew it-will get water seepage.The shaft is slotted,take a screw driver and give it a few turns with power off course.Try that.Grundfos is notorious for that.
stevemason5
10-12-2004, 12:00 PM
Thanks guys.
Looks like I scared oil lp man, sorry about that. I am not an expert but I have some tech backround, I listen pretty well and proceed slowly with great caution.
I did short out the TV and V terminals to test for C1 and C2 current. Before the jumping TV and V there was 120 VAC current at the C1 and C2 terminals but no circulator motion. After shorting out the TV/V terminals there was 0 VAC at the C1/C2 terminals and, of course, no circulator motion. Hope I did not fry something. If I did, I'll live with the consequences.
The 185 deg F shut down makes sense. If the circulator does not operate, the boiler heats the stagnate water near the aquastat themostat and shuts it down at the aquastat setting. Since the circulator does not supply colder water to the system, the heat in the water just builds up near the thermostat. I checked the aquastat setting - sure enough, it is set at about 180 deg F.
I am leaning toward the Grundfos UP 26-64F circulator as the core problem. If C1 and C2 are energized with 120 VAC during operation, why is the circulator not operating ?
I removed the silver shaft screw and turned the the shaft a few times. It seemed to turn pretty easily (I used a very small screwdriver). Then I energized the circulator with 120 VAC separate from the aquastat. I got nothing. No hum, no warmth or vibration on the circulator housing. Looks like a dead circulator or a dead starter. I called a Grundfos distributor. They no longer make this unit so replacing the starter circuit is out. Replacing the starter capacitor may be an option.
Questions:
Is there a test to check the circulator starter capacitor ?
This Grundfos has a pronounced hum that is transferred to the house via the radiators. Can anyone recommend a reliable and quieter replacement circulator that will fit in the above Grundfos installation ? A few rough dimensions: from flange to flange, the Grundfos is 6 1/2" tall and the flange bolts are 3 1/4" apart, center to center.
Thanks.
Steve
hetrola
10-12-2004, 02:26 PM
you more than likely have air in the system.
Do you have an air seperator such as a spiro-vent. You might have an air seperator above your expansion tank, and depending on your radiators you might have them there.
If some radiators are warm, follow the piping to the next radiator until you find a colder one, and remove the air. If you have trouble identifying the piping system call a pro.
The pump will make a little humming noise. If it resonates through out the house follow the pipe the pump is connected to and see if it is touching a floor joist. If it is put something between to absorb the sound.
epacertified
10-12-2004, 03:39 PM
I would imagine all ciculators fit.
I have been fooled by a bad circulator more than once
If you have a 120v at pump then there are only two things that can be wrong.
Air in the system(I,ve seen the best Plumbers have problems getting air out of some systems)
Bad circ motor(sometimes they start and two min later their not spinning any more and still have 120v present.
stevemason5
10-12-2004, 05:14 PM
Thanks again.
I did a few more tests.
On a cold start, everything worked except the circulator. There was 120 VAC at the circulator terminals on the body of the circulator. I heard and felt no humming on the circulator.
I took a risk and slowly opened the Grundfos at the dime-sized screw in the center of the circulator body. A little water came out. The shaft was not turning. I turned the shaft with a screwdriver to see if it would catch and run - it did not.
I tested the circulator for 120 VAC after the first premature shut-down (prior to reaching the room thermostat set temperature). It continued to show 120 VAC current even after shut-down (likely to continue circulating heat to the house). The boiler temp was 140 deg F. The aquastat set temp was about 180 deg F.
Its odd that the system shut down at 140 deg F before reaching the aquastat set temp of 180 deg F.
On the second cycle (again the room thermostat temp had not been reached) the boiler temperature reached almost 180 deg F with the aquastat still set at 180 deg F. I assume the aquastat senses a pre-set temp and when it is reached it shuts everything down. The circulator continues to run to distribute heat to the house (and cool down the aquastat till the next cycle).
None of my radiators was hot. Even the hot side pipes about 5 feet from the boiler were cold.
My opinion (which may be wrong) is that air in the pipes is not the main issue since currently the circulator is not operating. There is no flow so I cannot tell if there are any air pockets. Thanks for the "hum" advice. I'll check for joist contact and install some barriers.
I'm looking at a circulator by B and G, model NRG-22 I think. It has the same dimensions as the Grundfos. It seems pretty popular around here (Chicago) and the price looks right ($65). Is that a good choice ? This is a 3 BR, 2 bath, 2 story home.
I appreciate all the expert advice. Its very kind of all of you to spend some time to help out. Thank you.
Steve
slimwoodie
10-12-2004, 06:44 PM
probably $ 2300 worth of peoples time on this $ 115 dollar service call ..... just go and buy a $ 50 circulator, and be done with it ..if you had called a contractor, you woulda had heat long ago ....
hydronicsman
10-12-2004, 09:10 PM
The B+G would be dead last for my choice. They like to seize.
See if anyone has the Grunfos SuperBrute 3 speed. This pump is NOT your old one-no worries.. You can tailor the speed and pump curve to your system.
Taco's 00 series is the next best. The 007 probaly matches your old pump's performance.
Don't bother with the old pump's start cap..like Slim said, change the pump and be done.
stevemason5
10-15-2004, 06:22 PM
Thanks again.
Warning: LONG POST AHEAD
Looks like problem solved. It seems to be working well. Plus, I better understand my boiler set up. Thats important because I am responsible for this house plus two attached small apartments 24 hours a day, 7 days a week. I have often (but not always) had poor and often expensive advice/work in the past. I like to learn the facts before I decide what to do. If I called a contractor/plumber/electrician./repairmen everytime something went wrong, I'd be in the poor house.
TACO 007 vs. B&G NRF-22
A well known fact: The performance curves and prices on these two pumps are virtually identical.
I replaced my burned out Grundfos with a B & G NRF-22. I initially bought a TACO 007 (the Grundfos's were hard to find and expensive) but I had a lot of difficulty finding the right sized flange assy's for my set up. Really preferred to go with TACO. I heard they are a bit quieter, too. Still, the B & G has much, much better support around here. If it doesn't work out, I'll give B & G a hard time and replace it with a TACO.
B&G Reliability
I did a little research on the B & G circulator pump problem. From talks with distributors and a customer feedback rep at B & G there was a problem with the T or TR-100 series (something like that). I understand it been fixed. If it was not fixed, their whole product line reputation would be on the line. It would be pretty foolish not to fix it.
From what I hear, the water cooled pumps I looked at fall under the "throw-away" category. Not sure I agree. There are some replaceable parts. Not sure what I'll do next time.
A Short HVAC Story
My dad's new boiler system has a TACO 0010 circulator. But...
His old boiler set-up ran a long time before he had to replace it. He regularly oiled the old system's circulator pump (sorry, he does not remember the brand, he's 79 with a poor memory). He also tinkered with boiler settings making it much more safe and efficient. Prior to replacing the old boiler, the circulator pump was still there and still working, after 40+ years of operation.
Again, thanks for the help and patience.
Steve
hydronicsman
10-15-2004, 06:44 PM
Glad to hear you did ok:)
For the trades, changing out a 007 complete is more cost effective than fooling around with the parts that make it up-one call back would cost us more than it's worth.
Tip: if the system had a 3 piece circ like the Taco 110, and has zone valves, and you swap the 110 for a 007, sometimes you'll get banging of the zone valves after the swap. That's cause the 110's pump curve is more linear than the sharp ramp-up of the 007. Doesn't happen often, but sometimes..
I think you have a 3 year waranty on your new 007. Happy Hydronicking!
kenny3412
10-16-2004, 09:38 PM
go with b@g series 100 or high velocity depending on what you need. you can see coupler moving so you know its working. motor can be easily disasembled and motor and bearing can be changed seperatly, the coupler can also be changed, can really bring down repair costs. motor and bearing also has oilers so it wont dry up. should fit in location may have to replace mounts, ask distributor.
stevemason5
10-17-2004, 02:35 PM
Hydronics Man and other folks, thanks for the tips !
Another warning: LONG POST AHEAD
You are right, the B & G is warranted for 3 years. That was another reason I reluctantly switched from TACO. I think TACO's warranty is about 1 year. That should help in any immediate manufacturing quality problems. Still, I think most pumps from any manufacturer are designed to last well past the warranty period if you design the system well and install it right. Its the pump longevity that counts.
After I installed the B & G circulator I made sure it was filled with water and drained air from every system drainage location I could find. When I started up the system, I heard a kind of "washing machine" noise for about a minute. Then it settled down into a steady water flow with a quiet hum. I think I'm okay, but it scared me a bit.
I checked boiler parameters and the house radiators and all looks good so far. I'll just keep checking periodically. My tenants are pretty pleased, too.
I do not know how quiet the TACO 007 is compared to the B & G NRF-22. However, the new B & G is much quieter than my old Grundfos. A guilty confession: I actually prefer the low maintenance, water lub. pump design for this system. This house is almost 110 years old so there is always something to do. A zero to low maintenance pump is one less thing to worry about.
My dad's new boiler system is about 4-5 years old and warrantied, I think, so I'm pretty sure he's okay. He contracted one of the best (and $$$) firms in the area so if something happens, he won't have to fix it himself.
No need to write back. Just adding a little to the thread.
Thank you HMan, and thanks everyone !
Steve
tb7025
10-13-2005, 04:50 PM
Here is an odd question about the Taco Relay Zoning Board (SR504). If the 120VAC input into the relay is off will the board still relay the t-stat call from the zone to the boiler and just not be able to energize that zone's circulator?
GradyWhite244
10-13-2005, 10:05 PM
No, because the thermostat is powered by the SR504's transformer.
Black Adder
10-14-2005, 01:49 AM
Aw Gee I've got 120v at the pump but the pump is not working, what else do you think it would be but the pump? Next time call in a pro and have the damn thing fixed.
casturbo
10-14-2005, 12:23 PM
We used to put that B&G pump in all the time, until after 3 yrs of service they died. Realizing the old TACO 007's were still going strong after 15+ yrs of service, that's all we put in now (again). Hopefully, B&G has fixed their wet rotor design pumps so they match the 007 pump's superiority....always good to have another option. The B&G pump is a snazzy red color too!
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.