View Full Version : York millenium absorber, purge eductor



cperk
07-27-2010, 02:13 PM
Have York paraflow model ypc-fn-16sl-46-c-s-c with a high generator press. due to noncondensibles. Purge eductor is not working to send noncondensibles to the purge tank. We can purge from absorber to get quite a few bubbles for a few minutes, then it will quit. I know solution pump is moving solution because we can see it falling in low temp. gen. Any ideas will be appreciated because I'm stumped.

absrbrtek
07-27-2010, 02:51 PM
Are you purging from the absorber or the purge tank?

cperk
07-27-2010, 02:56 PM
Are you purging from the absorber or the purge tank?

Manually from absorber, but in auto we purge just from tank. I know the machine has air in it, but eductor is'nt working to pull noncondensibles from condenser, so that purge tank press. can increase.

klove
07-27-2010, 05:41 PM
#2 at Redstone MSIC?

cperk
07-27-2010, 07:20 PM
#2 at Redstone MSIC?

How did you guess?

klove
07-27-2010, 11:15 PM
Not because I got lucky.

If you want to, pm me and we'll get together and I'll fill you in on the history before you beat your head against a wall for no reason.