07-19-2010, 05:36 AM
trane rtac155 chiller system #2 comp has heavy noise on discharge line & oil seperator,load & loads normal ,compare to other system 10'f oil temp high,
can any one help me to eleminate this abnormal noise.reading is (mentioned below)taken at ambient of 113'f
Active Chilled Water Setpoint 45.6_°F
Active Current Limit Setpoint 102.0_% RLA
Evaporator Entering Water Temperature 51.7_°F
Evaporator Leaving Water Temperature 45.8_°F
Chilled Water Flow Switch Flow_
Chiller Top Level Operating Mode Running_
Circuit 2
Air Flow 100.0_%
Condenser Refrigerant Pressure 223.5_psi gauge
Saturated Condenser Refrigerant Temperature 138.1_°F calculated
Evaporator Refrigerant Pressure 39.3_psi gauge
Saturated Evaporator Refrigerant Temperature 44.2_°F calculated
Compressor 2A
Starts 14,706_
Supply Oil Temperature 177.0_°F
Intermediate Oil Pressure 211.6_psi gauge
can any one help me to eleminate this abnormal noise.reading is (mentioned below)taken at ambient of 113'f