08-31-2004, 07:20 PM
I have a Janitrol home cooling system,with a heat pump, my air handler is stored in the attic. The problem is that the freon line outside my house keeps freezing up. The air handler will not turn on. Now I can turn on the air handler manually and then turn the thermostat to cool and it will run and keep the house cool but it will run until I turn it off.If I switch to auto for the fan it will not turn on and the compressor outside will run continiously, freezing the freon line. Now this happens on hot days.In the evenings when it is cool outside the system runs with no problems. I have had a Hvac man come to the house, he checked the freon level and said it was good, he also replaced the thermostat. I am still having the same problems. Any ideas THANKS

cde72
08-31-2004, 07:30 PM
You have a complex mechanical issue within your air handler that will require a visit with a trained service technician...

glitho
08-31-2004, 11:05 PM
sounds like the t-stat to me

Senior Tech
08-31-2004, 11:11 PM
Ideas...yah...call a company that knows what they're doing...freeze up is being caused by the blower which is not running with the tstat in auto position...possible relay or wiring issue...and your now the proud owner of a new tstat that probably didn't need replaced.

obxrigger
09-01-2004, 05:43 PM
Originally posted by senior tech
Ideas...yah...call a company that knows what they're doing...freeze up is being caused by the blower which is not running with the tstat in auto position...possible relay or wiring issue...and your now the proud owner of a new tstat that probably didn't need replaced.

glitho
09-01-2004, 11:55 PM
Have a service tech come and check your blower speed and and also check to see if your evap coil is blocked. could be a restriction in the suction line. I'm not to sure with out looking at your system.

Senior Tech
09-02-2004, 12:17 AM
Originally posted by glitho
Have a service tech come and check your blower speed and and also check to see if your evap coil is blocked. could be a restriction in the suction line. I'm not to sure with out looking at your system.
Blower Speed...No
Evap Coil blocked...No
Restriction...No
Read the original posts again and give us 3 more guesses.

troyorr
09-02-2004, 07:42 AM
Is this an old furnace with a fan center and a combination fan/limit control with a manual switch? Could be the relay in the fan center. Or the cooling relay on a control board.

dodgedart401
09-02-2004, 11:37 AM
This problem could be many things, but even a ok heat pump guy should be able to find the solution! Make sure the fan switch is all the way into the auto position and not midway. If some cooling guy that does not like heat pump and does not understand them did it he could not have wired it correctly. All screws holding t/s to subbase must be tight. Could be 2 bad t/s also but not likly. Many hvac guys do not understand heat pumps wiring.

service guy
09-21-2004, 06:36 PM
Looks like you bought a new stat for nothing. It sounds like the system has been miswired also sounds like you need to find a new service company.

tech student
09-27-2004, 09:03 PM
Forget the freezing of your refrigerant lineset (piping) your unit seems to be miswired from tstat to airhandler somehow. Hard to tell without actually seeing whats going on. When you say your turning the unit on "manually" what exactly are you doing? Some programmable tstats have a 5-8 minute time delay..are you waiting to see what happens after you set temp at tstat?

mam123
11-21-2004, 10:49 AM
I saw this problem in reverse this summer - the blower ran continuously in on and auto position. The root cause was a faulty sequencer which Janitrol used as a fan relay. If that sequencer failed closed it is just as likely that yours failed open.

genman
11-22-2004, 07:17 AM
Looks like control problems - but i doubt its a fan realay - if he can turn on the fan from the stat the fan realy is working. Its gona take a tech that knows heat pumps to sort it out.
John

powpowtux
03-03-2006, 07:53 PM
I have the same issue. The tech says it is a motor issue, because the motor doesn't spin freely. It spins fine, one year later the problem is getting worse and i replaced the cap. but to no avail.

Maybe a relay?
Thermostat?

aircooled53
03-04-2006, 03:21 PM
Originally posted by obxrigger
I have a Janitrol home cooling system,with a heat pump, my air handler is stored in the attic. The problem is that the freon line outside my house keeps freezing up. The air handler will not turn on. Now I can turn on the air handler manually and then turn the thermostat to cool and it will run and keep the house cool but it will run until I turn it off.If I switch to auto for the fan it will not turn on and the compressor outside will run continiously, freezing the freon line. Now this happens on hot days.In the evenings when it is cool outside the system runs with no problems. I have had a Hvac man come to the house, he checked the freon level and said it was good, he also replaced the thermostat. I am still having the same problems. Any ideas THANKS


Sounds like your time delay relay to fan is bad.
1-2 N/O
1-3 N/C
Stuck in normal closed and without voltage from heat strip will not work auto in cool.

Goodman had several problems with this time delay, I usally just replaced with small relay and wired according to orginal wiring.

roesslerhw
03-04-2006, 08:25 PM
I would not think that it is relay problem. Usually the same relay is used if you are in auto or on with the fan switch. If you can manualy turn the fan on and off at the switch the relay or control module should be ok. I wonder if we really have all the details. Maybe you have a contactor at the outside unit sticking, making the ac continue running when the blower kicks off. That can sometimes be a intermitent problem. A experienced service tech should be able to look at the contacts and tell if there fried. If the refrigerent lines are froze outside then the coil inside is froze and you will not have airflow out of the registers. I have had many costumers mistake this for a blower not running. Just some ideas.

too tall terry
03-05-2006, 03:47 PM
Originally posted by glitho
sounds like the t-stat to me everybody says that one,but you should have it checked again,by a qualified tech.,not saying the guy was or was not,but Goodman's blower time delay relays are famous for sticking...just a thought

chillbilly
03-05-2006, 08:06 PM
OBX;
I am on the outer banks as well.
If you would like your problem solved, e-mail me and I'll get it fixed for you.