Crossed over from the residential side to the commercial side of the business about 2 years ago.Not much experience using a megger so any input would be greatly appreciated.
Came across a 10 ton trane roof top today,3 phase unit,208/230.Found nothing running-1st check was on secondary side of transformer and no 24vac.Checked primary side of transformer and was only getting one hot leg.Went to fused disconnect and found a bad fuse.Looked for any obvious burnt or shorted wires,ohmed loads to ground-ok.ohmed evap and condensor motor windings-ok.
When I ohmed out compressor with megger set to ohms only I was reading .5 ohms between common/start,common/run and run/start,I switched to megaohms on 500volt scale and put black lead to ground and tested each compressor terminal I got over 100 mega ohms on common and same for start and run.I'm assuming this is fine according to the manual.
I guess what I'm asking is did I do this right and are my readings acceptable.I did later find that on the contactor between L1 and L2 the plastic separator between contacts was cracked,wondering if maybe I was getting any arcing occasionally.I changed out the contactor and ran unit while I went over to another roof top issue and about 2 hours later unit still running.Fla on compressor was rated at 26 amps,when checked I was getting anywhere between 22 and 24 amps.
This was long,I apologize.Thanks so much in advance.Oh yea,if you get good readings on mega ohms-is there any need to go further with that compressor as for tesing?
Came across a 10 ton trane roof top today,3 phase unit,208/230.Found nothing running-1st check was on secondary side of transformer and no 24vac.Checked primary side of transformer and was only getting one hot leg.Went to fused disconnect and found a bad fuse.Looked for any obvious burnt or shorted wires,ohmed loads to ground-ok.ohmed evap and condensor motor windings-ok.
When I ohmed out compressor with megger set to ohms only I was reading .5 ohms between common/start,common/run and run/start,I switched to megaohms on 500volt scale and put black lead to ground and tested each compressor terminal I got over 100 mega ohms on common and same for start and run.I'm assuming this is fine according to the manual.
I guess what I'm asking is did I do this right and are my readings acceptable.I did later find that on the contactor between L1 and L2 the plastic separator between contacts was cracked,wondering if maybe I was getting any arcing occasionally.I changed out the contactor and ran unit while I went over to another roof top issue and about 2 hours later unit still running.Fla on compressor was rated at 26 amps,when checked I was getting anywhere between 22 and 24 amps.
This was long,I apologize.Thanks so much in advance.Oh yea,if you get good readings on mega ohms-is there any need to go further with that compressor as for tesing?