PDA

View Full Version : TCD150B300BD blower motor overheating



Gabrielnqn
08-24-2004, 07:51 PM
TCD150B300BD blower motor overheating

ok guys, here I am again....

I went to one of my clients the other day, this rooftop trane unit presented the blower motor overheating, and consecuently, the motor was turned off by the thermal protector, the coil was also ice blocked at that time.

I assumed that the motor was bad. And I proposed to change it. They agreed and I bought a replacement from the American Standartdealer down here.

The description between both motors, the old and the new one, were the same (but different brand, the old one was the original motor taht came with the unit from factory , I think "motortech" and the replacement they told me is the correct one is a marathon) as follows:

-208-230/460-3
-9.4/4.6A
-1745/1450 rpm
-thermally protected

After I replaced the motor, I spent 1 hr checking the correct function of the a/c unit and it was fine but today, two days later...I receive a call from my client complaining obut the unit...it was not working fine.

Actually, it presented the same symptoms as he first motor did. Overheating and the protector turning the motor off.

As a method for trying to find an answwer,,I measured the voltage/amps in other unit, same model and everything and the motor was using 6.2 Amps (9.3A said the mfg data)instead of 9.6A wich is using the new motor installed and 211V.

Then I found tat the contactor was not good, it showed like a shortcicuit at one of the terminals. I replaced it with a similar T-square 24V coil contactor.


The new motor installed continued using 9.6A @ 211V.

Any ideas? why is the new motor using 9.6A instead of 6.3A
The blower's axe seems to be fine...is in similar shape than the one in the other a/c unit where the motor is using 6.3A ...so I don't now what to do...maybe the contactor was the problem...but I am not sure....I think he is gonna call me tomorrow complaining again.

What to do? wait?

no8no3
08-24-2004, 08:44 PM
I'm wondering if the iceing has anything to do with it? do you suppose a return is blocked? Or maybe liner blocking inside the duct. If you dont get the airflow, you will increase your amp draw. With a multivolt motor like that one, it's easy to have it wired incorrectly. I'd check all those things as early as tommorrow, and dont make the customer call you. I am assuming this is a direct drive motor, but if wired right it should pull the correct amps.

Look at it this way, The unit HAS been running and now that the coil froze, it's pulling high amps. Or if it suddenly pulls high amps, the coil will freeze when off on overload....you will have to decide which of these it's doing. If both motors react the same, i doubt it's a motor problem.

Gabrielnqn
08-24-2004, 09:05 PM
the icing is a reaction b/c of the motor being disconected by the thernal protector...it doen not have to do with the motor high amps. The motor uses 9.6A all the time, and in all conditions.

rubobornot
08-24-2004, 09:16 PM
Is the blower a belt drive with the motor sheave at the same pitch diameter as the unit that is running the 6.2 A load? Is the supply duct static low and the return duct static high allowing the motor to run into the over amperage range. Is the voltage balanced between all three phases. Are there any bad spots in the wire or any connections that could cause the motor to single phase? extremly worn sheaves can bind up the belt and over heat a motor.

orland25
08-24-2004, 09:31 PM
firsd excuse my english, OK first I don't like that 211 volt. the original motor may be, but the new nooo. # 2 clean coil very very good. # 3check dampers #4how you see the fan ran low or fast. #5 locked the blade very close and compared with the other unit.#6 check dirt or oxid in wire,and put very hard.#7 elementary rotation. OK the you has low and discharge pressure ok.good luck

rob10
08-24-2004, 10:05 PM
Did you check the belt and all pulleys for wear? How much tension is on the belt? Is everything properly aligned? I have run across idler pullers that will seize up after running for awhile then turn freely. I believe this unit has a 2 pole contactor for the blower motor with the third leg wired direct. The contactor may have been a partial problem.

coastline
08-24-2004, 11:27 PM
you said this is a tcd150 how old is the unit /filters clean /if blower is pulling high amps all the time check the pulley sheaves probably spun all the way in that will increase amp draw on motor also make sure belt is not overtightened and straight listen for bearings may get resistive when hot causing amp draw

superfittertech
08-24-2004, 11:54 PM
Just a couple of dumb questions. Do you have the motor wired right, the right capacitor for the new motor, & the right speed tap? Did you replace the capacitor when you replaced the motor? Old trane motors had different wiring hook ups for 230 volt & 208 volt power input. Also if you had a frozen coil the amps would go down due to lower air flow if the fan is after the coil. But low airflow also could cause the motor to get hot do to lack of cooling over the motor. Is the new motor an open type frame?

Gabrielnqn
08-25-2004, 12:28 AM
rubobornot:

-The blower uses a belt drive motor sheave at the same pitch diameter as motor.
-The static low/high pressures (how to measure them?)
-The three phases are balanced +-5% between each other.
-No bad spots....the motor is using 9.6A all the time with 211V between each phase.
-sheaves ar normal wear, you can turn it with ur hand, turn it manually for 3 or 4 cycles and when you leave it, it wil only run for one full cycle.
-The belt is new B-62 and the tension is correct (not too much tension applied)

Orland25:

-There are 211V comming from the Panel. Same voltage is applied to the motors/compressors. The new motor's plate says 208-230V/460V-3ph
-Coil is clean.
-Dampers?...the air is moving fine across the ducts and running out from all the registers.
-The blower motor seems to be running fine, like 1750rpm
-Blades, are similar...same unit...unit was working 3 days ago, nobody changed the blades.


Rob10:

-belt is new, pulleys are fine.
-tension is fine.
-pulleys are aligned.
-yes, there is a two pole contactor (blue-red wires) and the black (common) wire is wired directly to the motor.
The amps between each other is almos the same.
-Today, I replaced the contactor which was damaged.


Coastline:

-Air filters are new.coil is clean.
-bearings are not like new...but it seem they are working, they dont presented movement when I tryed moving the axe.
-belt is fine and new.


Superfittertech:

-motor is wired right. It has a switch where you select from 230V (LO) or 460V (HI) inside the case. Of course I selected the "LO" position...then the wires go to 1, 2, & 3...easy connection. Used same wires that the old motor used. The new motor didn't come with the wires.
-NO capacitor, this is a 3-phase motor.
-Only LO or HI setting.
-I am thinking about the case you mentioned:

What if the freon charge (2 compressors) is not correct...and that causes the coil to froze, then the air flow will decrease, and the motor overheats???!!!

- The new motor is totally enclosed. Old motor was open frame.

Please continue with the replies....you are great guys!

superfittertech
08-25-2004, 01:13 AM
is the new motor TEFC (totally enclosed, fan cooled) or TENV. If it's the latter then wrong motor is installed. Usually blower motors are open frame, but you can use a TEFC in a dirty/wet environment & if the motor is TEFC then check the winding type ( a, b or f)

superfittertech
08-25-2004, 01:22 AM
other than that if amps are 9.6 unless you are using a true rms amprobe more than likely your amps are 10 to 11. Amps are too high if pulleys same size as an identical unit then the fan is trying to push too much air= possible broken supply & or return duct inside the buildind near the unit. How much outside air are you running at?

Gabrielnqn
08-25-2004, 01:26 AM
I will check tomorrow if this is a true replacement they gave me.

-I am using a Fluke 370 true rms clamp meter.
-pardon me...the pulleys are not the same size, the shafts are...pulleys seem to be:

(blower) 3:1 (motor) or more. They are the original pulleys. I checked the other unit.
Air flow seem to be fine.

superfittertech
08-25-2004, 01:48 AM
I meant are the pulleys the same size as the pulleys in the other unit. If so like I said earlier look for a broken supply duct.

rob10
08-25-2004, 06:32 AM
Originally posted by Gabrielnqn
TCD150B300BD blower motor overheating

ok guys, here I am again....

I went to one of my clients the other day, this rooftop trane unit presented the blower motor overheating, and consecuently, the motor was turned off by the thermal protector, the coil was also ice blocked at that time.

I assumed that the motor was bad. And I proposed to change it. They agreed and I bought a replacement from the American Standartdealer down here.

The description between both motors, the old and the new one, were the same (but different brand, the old one was the original motor taht came with the unit from factory , I think "motortech" and the replacement they told me is the correct one is a marathon) as follows:

-208-230/460-3
-9.4/4.6A
-1745/1450 rpm
-thermally protected

After I replaced the motor, I spent 1 hr checking the correct function of the a/c unit and it was fine but today, two days later...I receive a call from my client complaining obut the unit...it was not working fine.

Actually, it presented the same symptoms as he first motor did. Overheating and the protector turning the motor off.

As a method for trying to find an answwer,,I measured the voltage/amps in other unit, same model and everything and the motor was using 6.2 Amps (9.3A said the mfg data)instead of 9.6A wich is using the new motor installed and 211V.

Then I found tat the contactor was not good, it showed like a shortcicuit at one of the terminals. I replaced it with a similar T-square 24V coil contactor.


The new motor installed continued using 9.6A @ 211V.

Any ideas? why is the new motor using 9.6A instead of 6.3A
The blower's axe seems to be fine...is in similar shape than the one in the other a/c unit where the motor is using 6.3A ...so I don't now what to do...maybe the contactor was the problem...but I am not sure....I think he is gonna call me tomorrow complaining again.

What to do? wait?

After reading the motor nomenclature I noticed that it stated that 2 speeds were available. Which speed are you using. The higher speed will draw more amps.

jeffcolledge
08-25-2004, 07:48 AM
Just a thought...Is the new motor a condenser fan motor? Sometimes they will have all the same data, but will overheat as they are an "air-over" motor. This meaning that they use the air drawn through the condenser to cool them. Also, compare the weight of a blower, a belt and two pulleys to a single prop fan, that extra weight could also cause the over-amping you are experiencing. Ask your supplier if the new motor is intended for condenser fan or belted blower, just to rule it out of the equasion. Good luck.

Gabrielnqn
08-25-2004, 09:13 AM
The new motor is an similar shape/size/form as the old one which was installed. It has a flat base for mounting, same as the other motor.

coastline
08-25-2004, 05:35 PM
do you have a magnehelic check the static pressure it is possible that that unit uses and optional high static blower motor // if you put a standard motor in its place it would run but will pull excessive amps and get extremely hot in about and hour or two check the horspower either 3h/p or 5 h/p i believe

rob10
08-25-2004, 07:02 PM
drive pulley on the motor and adjust until you get an acceptable amp draw.

service guy
08-25-2004, 09:16 PM
Did you Check RPM on motor?? check no load RPM and then check with A load see what you get?? also what is the service factor rating on the motor?? It sounds like your not getting enough cool air to motor whats you return air Temp? Also that 211 volts is odd if you can check voltage to motor when it starts and when its under load see what voltages you get.

Gabrielnqn
09-01-2004, 07:33 PM
Well, it worked fine for 2 days, then the customer called me complaining again...well...

Finally I went there today, this is what I get:

Measured on motor terminals connector:
-211V no load / 205V under load
-4.6A no load / 9.2A under load

I seems the blower assembly is causing the motor to overheat and when the motor stops all the system fails and frezees.

but, why is that happening?

The bearings on the blower's axe does not seem to be so bad. Should I take the blower & aseembly out and fix it? (new bearings or bushings?)

service guy
09-01-2004, 08:48 PM
I think that motor is incorrect, First you said the old motor was open frame and the new was Totally enclosed I think there lies you problem less ventilation causes you to trip on overload but will usually take awhile to see I suggest putting in open frame motor and see what happens.

rob10
09-01-2004, 09:39 PM
You have an incoming voltage problem. 211 is low but 205 is way too low. In fact there should not be a difference between loaded voltage and unloaded voltage.

Gabrielnqn
09-01-2004, 10:15 PM
I am not sure, the other TCD150 has the same voltage applied and it is working fine, blower motor is 6.4A loaded and 4.3A w/ no load.

Also, remember I replaced an original motor which was overheating as this new motor is....same thing.
The original motor was fine, there is another problem here.
There is also good air flow across the motor casing.


I think if i put a new motor there it would use 9.X volts too.

Can it be the blower mechanism?

trane151
09-04-2004, 12:54 PM
High voltage terminal board in fan comparment may have loose connection. Are the panels on the unit when you are amping it out? I would guess you are moving to much air.

tj
09-04-2004, 01:54 PM
Did you check the amps when you replaced the motor? Was it pulling 9.6 from the get go or was it lower?

Gabrielnqn
09-04-2004, 06:31 PM
The old motor's current consumption was the same as the new one...9.3A under load.

Thats why I think the motor is not the problem here.

Amps:

no load= 4.6A
under load= 9.3A

keywest
06-08-2006, 12:20 AM
sounds like a bad electrical connection somewhere.or the blower is under alot of strain from the pully assembly

kentucky hillbilly
06-08-2006, 07:21 AM
Check your molex connector

coldndn
06-08-2006, 05:43 PM
check the other motors to see if they have specific low voltage taps. it sounds to me that your replacement motor is either 230 or 460 volts instead of 208/230/460. if all you have is a tap for 230 or 460, your problems lie within the motor itself and due to the low incoming voltage you are increasing your amps that way and not with the sheave position. or its possible that you fully did not switch the volt setting from 460 to 230. remember volts down amps up

needlevalve
06-08-2006, 09:17 PM
You need to multipy the SF x Hp to determine motor size.
Trane over sizes the moter with higher service factors.

Ex. 3/4 hp with a 1.35 service factor = 1hp

Universal 3/4 hp with a 1.00 sf = 3/4 hp


That why you have to order thru trane or oversize new motor.

good luck

duke of earl
06-08-2006, 09:35 PM
I read a response by someone who said that if the airflow were blocked that the motor would overamp. If the return duct were restricted, the amps would be reduced because the fan would require less horsepower. If too much air is allowed to enter the fan, the motor will overamp. I suggest you choke down your return air and see if it affects the amp draw. If the amps come down then investigate the return ductwork and economizer to see if you are getting too much air. Plotting the fan performance on a graph provided by the manufacturer will tell a lot about airflow, horsepower, and static pressure. Also measure your external static pressure (fan outlet static minus fan inlet static. If it exceeds the nameplate then you have too much friction for the given horsepower of the fan.